How to adjust the zero & span of a control valve from the
posiitioner(MIL)?
Answer / ashish b. patel
when you are open the positioner there are two setting, zero & span. positioner to give 4 mA and set the Zero adjust and valve should be 0% open. after give 20 mA and set to span and valve should be 100% open. this to adjust are very important. after you can give again 4 mA- 0%, 8 mA- 25%, 12 mA- 50%, 16 mA- 75%, 20 mA-100%.
| Is This Answer Correct ? | 9 Yes | 0 No |
What is the compensation of thermocouple
How to convert gpm into inches of eater.I nerd formula with example so pls help me.
what is the si unit of pressure?
6 Answers HTA Instrumentation,
i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me
what is the difference between profibus and controlnet networking.
What is the GK Value in Flowmeter?
what is the significance of hook up
wht is loops ? how many loops are there?
why we take 4 to 20 mA as out put of every instrument like pressure transmittre ?why we cant take 0 to 20mA as output?
WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
What is an analog input-output
10 Answers TN, Torrent Pharma,
can we copy the software from a transmitter using hht(hart 275) ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)