Answer / venkatesh sk
below 5hp motor used dol 5to 15hp motor used stardelta
starer
| Is This Answer Correct ? | 114 Yes | 21 No |
Answer / pawan dahiya
DOL using gange normal used 5HP and 5HP to above used in
star delta. Because 5 HP above value without star delta
motor/pumps starting time requied power(yani three gunaa
reating ki)
| Is This Answer Correct ? | 38 Yes | 3 No |
Answer / prakash suhane
There is no hard N fast rule which state the range of star
delta and DOL starter, we have to keep in mind fallowing
points during configuration of DOL starter.
1) Motor should not be of very high rating.
2) Starting torque (reqd to start motor)is not very high.
apart from above case we should use star delta starter.
| Is This Answer Correct ? | 25 Yes | 6 No |
Answer / nani
Now a days we are using DOL starter up to 3ooKw, it can
possible, already we are working in this system.
| Is This Answer Correct ? | 23 Yes | 10 No |
Answer / pawan dahiya
Normal Dol Rang less then 5 HP and Star Delta Used Normal
5 HP to 15HP
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / rajkumar saini
below 5 hp using DOL starter & above 5HP using star delta
starter
| Is This Answer Correct ? | 13 Yes | 7 No |
Answer / bikash bhagat
the range of using dol starter is under 5 hp & above 5 hp we can use star delta starter because when we start the motor the starting current is inreases 5 to 7 times than the rated motor full load current so it should effected the motor thats why above 5 hp we use star delta starter
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / rangaraj
dol starter is us 5hp motor(3.5kw)in direct current.star delta starter is us above 7.5hp starting current high in star and delta delta reduced 3-4 times voltage.dol connection star and delta connection delta.... rangaraj015@gmail.com
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / pawan
Till 5HP motors we use DOL starters . If we use beyond it,there will be a drip in the mains power supply.. Beyond 5HP, star delta is use as firstly motor operate in delta and thus its starting voltage is less(which is req. as in starting no back emf is there) after an instant it start operating in star as now motor has developed sufficient back emf to counter the voltage. Now the current is less(I/root3) as less current is beneficial reducing losses.. Now the ques. arises why only 5HP?Why not 5.2 or 5.5? The answer is its just a standard value.When it is tested beyond 5HP, drip is showing.. Thus the value 5HP.. Also motor are not available as 5.2 or 5.3 HP..So the standard value taken is 5HP...
| Is This Answer Correct ? | 2 Yes | 4 No |
Difference between hopkinson and swinburne's test
what is self commutation how a thyristor discharges through a capacitor and inductor
What is static frequency control used in gas turbines
what is NGR in generator?
6.6 KV /.415KV Step down trf. we can get 6.6 KV from primary by applying .415 KV secondary side by same TRF.
what is the function of anti-pumping in circuit breaker?
20 Answers Aditya Birla, INEL, NCC,
Why celling fan rotates in anticlockwise direction and table fan in clockwise direction ? Give technical reason.
hello! can anyone explain to me how a 3 speeds table fan work? what are the factors that are controlling the speed of a normal table fan? Is it by varying the voltage or changing the magnetic field? would appreciate your reply :) thx in advance.
What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?
If a HV Underground Cable (13.8KV) is layed in the ground below 1.5 Mtrs and any building construction is done on the Cable route. IS this allowable or Not? What should be the clearance. As per ISO construction on HV cable route is safe or Not? Why? Can any body suggest the site for my question?
WHY THE TRANSFORMER VALUE MEASURES IN KVA INSTEAD OF KW.
what is the safety of ACB & VCB and how can this work and how can the service the ACB & VCB parts name with picture
21 Answers ABB, ACB, Bharti, Claris Lifesciences, Honda, L&T, RotoPower, Sterling Wilson, Wipro,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)