what is the range of using dol starter & star delta
starter.
Answer Posted / bikash bhagat
the range of using dol starter is under 5 hp & above 5 hp we can use star delta starter because when we start the motor the starting current is inreases 5 to 7 times than the rated motor full load current so it should effected the motor thats why above 5 hp we use star delta starter
| Is This Answer Correct ? | 6 Yes | 4 No |
Post New Answer View All Answers
2. A current i=(10+10 sin t)amperes is passed through MI type ammeter. its reading will be.........
how make megger test for control cable like 12c x 1.5mm and what it apply voltage and test timing details.
What is different bewteen low or high impedance busbar protection scheme
If symmetrical fault occurs at the terminal of a synchronous motor then how the motor will act...explain it..
how many electricity poles are there and what are the names and their sizes.
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
what are the applications of TIG welding
Leakage current,un balance current which relay using for high voltage transmission?
why does make gain margin and phase margin on same plot.?
What is the magnetic field (coil DC ) of Turbo Expander?
How the setting of the vector surge relay shall be calculated when the relay is to be used for Grid islanding application?
Why is remote backup preferred to local backup?
I meggared my 2c*70 sq mm AL AR XLPE cable. its one end show 50 M ohm . is my cable is safe for laying. I have only one phase and neutral.
How to select transmission line type (i.e. 11kv or 33kv) for new established industries
What are PLC leader logic program method