why CT output is always raetd 5.regardsof primery curre.
Answers were Sorted based on User's Feedback
Answer / balu
There are two CT output current. 5A or 1A. These are
standard outputs.There many measuring and protective
instruments will be connected to this secondary. So these
instruments designed for the output of this current. Based
on the customer primary current, the multiple factor can be
programmed to measure primary current. So, it reduces
customization .
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / ashish gupta
It consider to be standard. But if we see the ratio error and phase angle error formula we observe that turns ratio ns comes out to be in denominator.So higher the turns ratio lower is the error. So higher turns ratio is obtained when secondry current is 1 amp
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / mukhesh
bec from t/f see relese the cts primary curent and
transfoemer ratio will give the exact 5a if any fault o
tr line the ratio willt if open will burnt ou be other
than 5 a ansd seec should not open at any time
| Is This Answer Correct ? | 3 Yes | 5 No |
what is meant by frequency ?
what is the VA(Voltampire)? define with calculation?
When VFD is connected to a 3 phase main supply there is load current difference between incomer to VFD and outgoing from VFD.
The safest value of current which can pass from human body?
I have 1 KW, 3ph. 440v, 50 hz, cos(phi) .75, efficiency 75%(star delta connection)Motor. How to calculate line current & Phase current (1) Star connection (2) delta Connection
I WANT BHEL PREVIOUS QUESTION
how to calculate Transformer loss?
How DC earth leakage currents can be reduced ?
in three phase 11kv transformer (11kv/433v) input( R,Y,B) output (X,Y,Z,N) the connection as follows 1 phase R -open 2phase y connected to both R and y of input] 3phase B- B what is the output voltage X to N ,Y to N , Z to N
what are the insulation properties.
2 Answers Cable Wireless, MAHINDRA,
Is there any reason that a vertical motor can not be mounted horizontally ? I happen to have one and would like to use it horizontally to save money by not buying a new horizontal motor.
how do you choose the cable size as per amps rating & the voltage drop for the same.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)