Answer / basit
for long distance and more accuracy we use 3 or 4 wire RTD
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shani_dms
depend on distance if distance too short its should be two
wire
3 and 4 wire used for long distance
| Is This Answer Correct ? | 9 Yes | 5 No |
Answer / rashidmanzoorkt
If the distance between transmitter and RTD is not long,Any
rtd (2,3 or 4 wire)is suitable.
| Is This Answer Correct ? | 10 Yes | 7 No |
Answer / bhardwaj**
generally pt100 3-wire rtd is used as third wire
compensates the error and maintains the accuracy of
measurement system
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / s vedpathak
3 wire RTD (PT100)is good compare to 4 wire & 2 wire as the
lead wire compensation is achieved in it with less cost.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / ashish namdev, bina refinery [
3 & 4 wire rtd use for temp. compensation from sensor to Tx.
3 wire is good & mostly use.
4 wire is best because in 4 wire, both wire(+ & -) have
compensating cable. then reduce unwanted temp. approximate
negligible. then get correct output.
2 wire have more temp. interference error.
| Is This Answer Correct ? | 2 Yes | 1 No |
3 wire rtd is good bcz thired wire is used to compensate
wire resistence it is a wheet stone bridge
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / m.murali- inst.technologist
Balance two wires are used for compensation, if no. of
compensation cable increases ie compensation resistance become
average.
| Is This Answer Correct ? | 2 Yes | 8 No |
in my plant 100% feedwater control v/v is air to close but due to instrument air fail,the valve opens but instead of drum level high its get tripped in low low drum level.the urv of level tx is 0 and lrv is -800.pls tell me the reason. for such behaviour.
WHAT IS DIFFERENCE BETWEEN TWO WIRE RTD AND THREE WIRE RTD?
WHAT IS THE MAIN WORKING OF BOILER.
How to calibrate H2s Dectector
how will you check torque value during Factory acceptance Test for control valve/ESD ON/OFF VALE how will you confirm this torque value is being correct, Which document will you be refer.
I am manjunath having exp in maintenance of chemical plants,know i want to do a design course INTOOLS,after doing design course can we get jobs in design field.sinve i dont have design exp..
What s the exact height of installed transmitter?
pls tell me whethere flame proof HMI's are available or every HMI is manufactured by considering flame proof standard.
How we can do the linearity test for Bently Naveda Vibration Probe?
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.
Explain the working of rota meter.
Why we use the double acting control valve in flow line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)