HOW DO A DISTANCE RELAY SENSES THE FAULTY ZONE.
Answers were Sorted based on User's Feedback
Answer / amit sharma
distance relay operates on the zone impedance. If impedance
seen by the relay in the zone is less than the rated imp.
then relay trips and the zone is isolated.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / d ramesh
Distances relay senses the faulty zone if impedance seen by
the relay is below the set value then it operates and
isolates the faulty zone.
z=v/i below the set, then operates
zone1= 80% of protected line
Zon2=100%protected line + 50%shortest line
Zon3= 100%protected line + 100% longest line.
| Is This Answer Correct ? | 12 Yes | 3 No |
Answer / sukhvinder
relay works is ratio of voltage over current.line is
divided into zones zone 1,2,3. zone1 is 80 per of line and
set for immediately trip for line
| Is This Answer Correct ? | 12 Yes | 4 No |
Answer / limbian
Distance Protection Relay senses the faulty Zone by
recieving signal from Voltage Transformer
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / j.kesavan
it is sense sending end receving end voltage relay trip
depending upon voltage.
| Is This Answer Correct ? | 5 Yes | 24 No |
why incomer bay is required before transformer bay if there are more than 1 nos. of transformer bay.
Do you know how to measure the earth resistance?
What is the difference between alternator and generator?
HOW VFD USED IN ENERGY SAVING
wat is d diffr btw shunt coil and trip coil in VCB?
how to select cable size?
if 40 watt bulb has higher resistance then a 100watt bulb then according to joul farmula p=I^2R the 40 watt bulb more power consume then 100 watt bulb.
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase, before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
what is two point starter?
how to calculate diesel consumption of a D.G.Set?
What is the safety of UPS?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)