HOW VFD USED IN ENERGY SAVING
Answers were Sorted based on User's Feedback
Answer / suresh
VFD – variable frequency drive..
VFD is useful in energy saving because it reduces the
motor speed as demand decreases.When the speed is reduced
the power consumption Will also reduce because ,
Power = (speed)3 {cube of speed}
For example if the speed is reduced to 80% of the maximum
value the power consumed will be reduced by 50%
Power consumed = (0.8)3 = 0.512 = 51.2%
Is This Answer Correct ? | 108 Yes | 8 No |
Answer / manoj patel
VFD drive controll speed of motor by varing its freq.
But at varing freq. it have to maintain V/F ratio
constant.So for reducing speed it have to reduce freq.but
its also maintain V/F ratio constant.So automatically its
voltage is reduced.
So powre is depends on V, I & PF. So its save energy..
Is This Answer Correct ? | 30 Yes | 4 No |
Answer / rahul
Practically VFD helps to save enery in Variable torque
loads only like Fan , pump. With affinity laws Power
proportinal to cube of speed, so if speed is reduced you
will get energy saving by using this law.
For constant torque application , if your process speed is
not full RPM but less than that say 30 Hz , then energy
saving will be there by using VFD, as you are not required
to run the motor at full speed.
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / mashood
The real saving is observed when the VFD is used on input reference of temperature, pressure, differential pressure etc.,and this is more significant in case of Fans and Pumps, specially when we calculate the energy consumption over a certain period of time where different temperature and seasons are involved.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / tilak guruge
vfd is help to reduce the power consumption and saving the life time is motor and other related pats of the pump.basically vfd is control the motor speed and its give command to the motor as a demand
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / itc ltd, snacks ,haridwar
Drive function is power convert,one way to onother way(by
phase convertor)So improve the power factor,
Is This Answer Correct ? | 24 Yes | 38 No |
What are the Formula of computing Back up Time of 500kVA UPS with 4 Battery Banks, each bank composed of 43 pcs of Batteries 12V150Ah. How to compute the Back up Time of UPS? We have also 3X500kVA UPS running in Parallel same composition as I write above.
Brief working principle of stabilizer,application & safety precautions
what is the difference between potential transformer and capacitive voltage transformer?
What is hysteresis losses?
what are the type of motors
Why 11kv to be generated in generation station
0 Answers TNEB Tamil Nadu Electricity Board,
What technology is used in latest generators?
What is speed mode?
three phase 180kva diesel generator can take how much load in amp and what is formula to get this?
what is the function of anti pumping relays? what is KVAR? How it is generated in alternator? What is 3rd Harmonics? What is IDMT relay?
What is the difference between electric and electronic circuits?
what is the pi test for current transformer?