HOW VFD USED IN ENERGY SAVING
Answers were Sorted based on User's Feedback
Answer / suresh
VFD – variable frequency drive..
VFD is useful in energy saving because it reduces the
motor speed as demand decreases.When the speed is reduced
the power consumption Will also reduce because ,
Power = (speed)3 {cube of speed}
For example if the speed is reduced to 80% of the maximum
value the power consumed will be reduced by 50%
Power consumed = (0.8)3 = 0.512 = 51.2%
| Is This Answer Correct ? | 108 Yes | 8 No |
Answer / manoj patel
VFD drive controll speed of motor by varing its freq.
But at varing freq. it have to maintain V/F ratio
constant.So for reducing speed it have to reduce freq.but
its also maintain V/F ratio constant.So automatically its
voltage is reduced.
So powre is depends on V, I & PF. So its save energy..
| Is This Answer Correct ? | 30 Yes | 4 No |
Answer / rahul
Practically VFD helps to save enery in Variable torque
loads only like Fan , pump. With affinity laws Power
proportinal to cube of speed, so if speed is reduced you
will get energy saving by using this law.
For constant torque application , if your process speed is
not full RPM but less than that say 30 Hz , then energy
saving will be there by using VFD, as you are not required
to run the motor at full speed.
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / mashood
The real saving is observed when the VFD is used on input reference of temperature, pressure, differential pressure etc.,and this is more significant in case of Fans and Pumps, specially when we calculate the energy consumption over a certain period of time where different temperature and seasons are involved.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / tilak guruge
vfd is help to reduce the power consumption and saving the life time is motor and other related pats of the pump.basically vfd is control the motor speed and its give command to the motor as a demand
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / itc ltd, snacks ,haridwar
Drive function is power convert,one way to onother way(by
phase convertor)So improve the power factor,
| Is This Answer Correct ? | 24 Yes | 38 No |
What will be the size of copper cable (each for 3 phase and 1 neutral) from Service connection Kit-Kat to Panel Board (i.e. to main switch) for a 6 pole 3-phase AC induction motor of 200 H.P. capacity? Amp-255 A, Frequency:- 1450 rpm.
about your self?
4 Answers Hyundai, US Technology,
why the NGR (neutral grounding resistor) always OFF during DG off?
What is the formula of frequency ?
How the annunciator works ? How to do its wiring
WRITEDOWN FEW RELY CODES
If you touch power transformer........ Then , in your body current will flow or not...?
What happened when the field winding of dc series motor is open?
I have a 380 KVA DG set. How can i find out 1. My Fuel Consumption per hr ? 2. Electricity produced in 1 Hr. ? 3. If load varies then how does it affect fuel consumption & electricity produced ? Please HELP !!! Really need an answer.
how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???
what is the response time of relays when a FAULT OCCURS IN A POWER SYSTEM?
Why the power factor improvement is so important in industrial loads
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)