Do you know how to measure the earth resistance?
Answers were Sorted based on User's Feedback
Answer / zahid ali
Dear Friend
the R = Pl/A is not used to measure earth resistance. is is
used to measure conductor resistance.
to measure earth resistance. We need an DC power source,
Ampere meter & volt meter & the formula R = V/I
The earth resistance testers are available in market, they
are been used by three leads on connected to the test
object & Current & Potentional probes are conneceted 20 &
10 meters away from object under test.
| Is This Answer Correct ? | 20 Yes | 1 No |
Answer / ullas
using two methods:
1.fall of potential method
2.earth tester(device)
factors affecting earth resistance are
1. Shape & material of the earth electrode.
2. Depth of the electrode at which they r burried in soil.
3. Specific resistance of the soil surrounding the electrode
(Specific resistance of the soil varies depending on
moisture content in the soil..... varies from 80*10^3ohm-m
to 80*10^6ohm-m)
| Is This Answer Correct ? | 18 Yes | 2 No |
Answer / sandesh
To find the earth resistance we basically need to do the
resistivity test of soil which is symbolized by rho.Now as
per IS we need to have mutual earth resistance below 1 ohm.
so to find the earth resistance for different type of
earthing i.e. plate and pipe we need this resistivity which
vary place to place. for a detailed derivation for both
earthing method and calculation for resistance by one
earthing please refer IS 3043
| Is This Answer Correct ? | 0 Yes | 1 No |
to mesure the earth resistance we need to find a specipic
constant of the earth soul.
so by using a formula.
R=P(L/A) Ohm
where,
p = Secific gravity constant
L = lenth of Earth
A = Area of Earth.
| Is This Answer Correct ? | 1 Yes | 30 No |
WHY IS THE POWER FACTOR NOT MORE THAN UNITY.
What must be the minimum distance maintained between 2 Generators as per International standards?
How to select HT/MV cable size ?
for a machine R=130 KVA Y=132 KVA B=144 KVA Then what will be the total kva
What is surge impedence and surge loading....???
Why transformer rating is represent in KVA?
7 Answers Bhel, Sonalika, Usha Martin, Wipro,
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
What are the tests to be conducted in the electrical installations
In Power cable specification what is U0/U and Um.
In how we connect watt meter for open & short circuit test of a single phase transformer.
What happens if the Capacitive Voltage Transformer Primary neutral is not earthed. There is a CVT between Transformer and source, and the CVT neutral of the transformer is not earthed, does it effect the transformer while charging or does it effect the transformer charging process.
control diagram of star delta starter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)