1. find load.... 8kw shower
2. find current Power/voltage ie. 8000/230 =34 amps
3. Use next fuse size up from current...40amp fuse/breaker
4. select a size cable suitable to carry 40amps
5. Find length of run. ie 20 meters.
6. carry out volt drop calculation
design current (34amps) x Length of run (20 meters) x
millivolt drop per meter (7.83 mvolts/meter for 4 square
cable) >>> 34 x 20 x 0.00783 = 5.44 volt drop!
if volt drop exceeds 9.2 volts use bigger cable
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / peer
If we know power calculate I(current) then select Breaker
and choose cable according to that.
Ex: Power is 50KW 3Ph supply.
I=100A (Apprx)
Breaker size for the above is 4c.35 sqmm+1c 16sqmm
E.C.C.
| Is This Answer Correct ? | 20 Yes | 9 No |
Answer / vzvodator
See this program -
http://miroshko.kiev.ua/cablesel/wiresel_mini_en
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / iftekhar mahmud
Caterpillar generator produce (Two generators) 127*2=254 amp
at 11 kv .
What would be the cable size (XLPE) to supply 256 amp at 11
kv? Air or surrounding Temperature is 32 degree C. Cable
will go under ground at 2.5 feet depth. Group Rating Factors
is 3 cables. Clearance between cables is 7 cm. Soil
Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2
K.m/W
I would like to use 3 separate single core instead of using
3 core cable.
Some says I should use three separate single core 120RM cables.
Some says 70RM .some says 95.
I m totally confused.
Is there ant specific rule to determine cable size?
Ifte
My e mail address is ifte13@yahoo.com
Anyone please send me the answer to my e mail address,
i will be very glad.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / vijay shinde
it simple it should be select on how much current will
cable carry
| Is This Answer Correct ? | 6 Yes | 13 No |
Answer / ahmed bilal
for calculating cable load, you have to email me
aoabilal@gmail.com
| Is This Answer Correct ? | 4 Yes | 17 No |
Answer / ashutosh tiwari
according to kelvins economic choice of conductor size
formula is
total cost = (P1+p2*a)+p3*a
a>>>conductor size
| Is This Answer Correct ? | 14 Yes | 30 No |
I have 200 KVA Isolation Transformer for UPS input side. & ups was having 48% load, suddenly got short what will be the reason.
advantages of vvvf drives over non vvvf drives for EOT cranes
IS THERE ANY ELECTRONIC CIRCUIT TO REDUCE THE NEUTRAL TO EARTH VOLTAGE BELOW 3V ?
What is the relationship between the sending end and receiving end?
Role of active and reactive Power sharing in between two synchronized Generators, Droop Setting role ?
how to find the Motor,s insulation Power?
pls tell me function of closing coil of A.C.B.
What is the method to solve circuit using source transformation?
Define protection core in CTs Ex. 5P10, 5P20 etc.
is it possible to flow currnet between earth and nutral wire in a circuit???
Which fault is caused by lightening and thuderstorm a. Line to line fault b. Single line to ground fault c. Double line to ground fault
Capacitor panel CT is normally fixed on Y phase of the main panel.why???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)