Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to select cable size?

Answers were Sorted based on User's Feedback



how to select cable size?..

Answer / itsme

1. find load.... 8kw shower
2. find current Power/voltage ie. 8000/230 =34 amps
3. Use next fuse size up from current...40amp fuse/breaker
4. select a size cable suitable to carry 40amps
5. Find length of run. ie 20 meters.
6. carry out volt drop calculation

design current (34amps) x Length of run (20 meters) x
millivolt drop per meter (7.83 mvolts/meter for 4 square
cable) >>> 34 x 20 x 0.00783 = 5.44 volt drop!

if volt drop exceeds 9.2 volts use bigger cable

Is This Answer Correct ?    23 Yes 5 No

how to select cable size?..

Answer / peer

If we know power calculate I(current) then select Breaker
and choose cable according to that.
Ex: Power is 50KW 3Ph supply.

I=100A (Apprx)

Breaker size for the above is 4c.35 sqmm+1c 16sqmm
E.C.C.

Is This Answer Correct ?    20 Yes 9 No

how to select cable size?..

Answer / vzvodator

See this program -
http://miroshko.kiev.ua/cablesel/wiresel_mini_en

Is This Answer Correct ?    4 Yes 0 No

how to select cable size?..

Answer / iftekhar mahmud

Caterpillar generator produce (Two generators) 127*2=254 amp
at 11 kv .
What would be the cable size (XLPE) to supply 256 amp at 11
kv? Air or surrounding Temperature is 32 degree C. Cable
will go under ground at 2.5 feet depth. Group Rating Factors
is 3 cables. Clearance between cables is 7 cm. Soil
Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2
K.m/W


I would like to use 3 separate single core instead of using
3 core cable.

Some says I should use three separate single core 120RM cables.
Some says 70RM .some says 95.
I m totally confused.
Is there ant specific rule to determine cable size?
Ifte
My e mail address is ifte13@yahoo.com
Anyone please send me the answer to my e mail address,
i will be very glad.

Is This Answer Correct ?    4 Yes 3 No

how to select cable size?..

Answer / vijay shinde

it simple it should be select on how much current will
cable carry

Is This Answer Correct ?    6 Yes 13 No

how to select cable size?..

Answer / ahmed bilal

for calculating cable load, you have to email me
aoabilal@gmail.com

Is This Answer Correct ?    4 Yes 17 No

how to select cable size?..

Answer / ashutosh tiwari

according to kelvins economic choice of conductor size
formula is
total cost = (P1+p2*a)+p3*a
a>>>conductor size

Is This Answer Correct ?    14 Yes 30 No

Post New Answer

More Electrical Engineering Interview Questions

why we use the fuse in only one wire? althrough in ac current the current flows in both directions. why the neutral wire can be taken half the magnitude of phase wire while same current returns from neutral wire?

2 Answers   Bhel,


why capacitor rating measure in KVAR. ?

2 Answers  


why transformer ratings are taken in 11kv 22kv 33kv but not in 10,20,30kv

5 Answers   ushacomm,


Explain what cmos is and its benefits?

0 Answers  


why we cant use AC supply products in DC supply?

21 Answers  


how to calculate multiplying factor with ct ratio 400/5

1 Answers   KBPL,


When one of three series resistors is removed from a circuit and the circuit is reconnected, the current

1 Answers  


what is the impedance voltage of transformer?

1 Answers   AVI Enterprises, MacLellan,


1 amp means-how many electron flow per second. ?

2 Answers  


WHAT DO YOU MEAN THE DIFFERENT TYPE OF CURVES OF RELAY LIKE STANDARD INVERSE, VARY INVERSE, NORMAL INVERSE, LONG INVERSE ETC....

0 Answers  


how withstand of hi-pot test outputs of transformer wire 2.5mm

0 Answers  


Which motor connection is preferable star-delta or delta-star?

0 Answers   IOCL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)