how to select cable size?
Answers were Sorted based on User's Feedback
Answer / itsme
1. find load.... 8kw shower
2. find current Power/voltage ie. 8000/230 =34 amps
3. Use next fuse size up from current...40amp fuse/breaker
4. select a size cable suitable to carry 40amps
5. Find length of run. ie 20 meters.
6. carry out volt drop calculation
design current (34amps) x Length of run (20 meters) x
millivolt drop per meter (7.83 mvolts/meter for 4 square
cable) >>> 34 x 20 x 0.00783 = 5.44 volt drop!
if volt drop exceeds 9.2 volts use bigger cable
| Is This Answer Correct ? | 23 Yes | 5 No |
Answer / peer
If we know power calculate I(current) then select Breaker
and choose cable according to that.
Ex: Power is 50KW 3Ph supply.
I=100A (Apprx)
Breaker size for the above is 4c.35 sqmm+1c 16sqmm
E.C.C.
| Is This Answer Correct ? | 20 Yes | 9 No |
Answer / vzvodator
See this program -
http://miroshko.kiev.ua/cablesel/wiresel_mini_en
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / iftekhar mahmud
Caterpillar generator produce (Two generators) 127*2=254 amp
at 11 kv .
What would be the cable size (XLPE) to supply 256 amp at 11
kv? Air or surrounding Temperature is 32 degree C. Cable
will go under ground at 2.5 feet depth. Group Rating Factors
is 3 cables. Clearance between cables is 7 cm. Soil
Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2
K.m/W
I would like to use 3 separate single core instead of using
3 core cable.
Some says I should use three separate single core 120RM cables.
Some says 70RM .some says 95.
I m totally confused.
Is there ant specific rule to determine cable size?
Ifte
My e mail address is ifte13@yahoo.com
Anyone please send me the answer to my e mail address,
i will be very glad.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / vijay shinde
it simple it should be select on how much current will
cable carry
| Is This Answer Correct ? | 6 Yes | 13 No |
Answer / ahmed bilal
for calculating cable load, you have to email me
aoabilal@gmail.com
| Is This Answer Correct ? | 4 Yes | 17 No |
Answer / ashutosh tiwari
according to kelvins economic choice of conductor size
formula is
total cost = (P1+p2*a)+p3*a
a>>>conductor size
| Is This Answer Correct ? | 14 Yes | 30 No |
I had applied for JE in PSEB, Can you pls send me the Question bank for related to my field
explain me the relation between torque, frequency,speed,voltage and current in the 3 phase induction motor?
Dear sir, I have completed DECE in the year 1995. I have work experience in HT and LT LINE more than five years. Now i am doing BE in EEE from rajasthan university. After completion of BE,can i apply "C" Licence sir? Please reply.
how is working bearing heater?
WHAT IS REACTIVE POWER?
What are protections for dty type transformers
what are the main parts of DG? explian thier functions?
8 Answers Apollo Power, Tata DoCoMo, Tyco, Vizag Steel,
why the current leads voltage in the case of a capasitor
what is mean by VCB colour code..???
how many testing use in power transformer?tell equipment names?
can a 12v dg starting battery(150 AH) be replace by 6 nos of 200AH batteries each of 2v connected in series.
How will you explain transformer action in case of 3-phase induction motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)