how to select cable size?
Answers were Sorted based on User's Feedback
Answer / itsme
1. find load.... 8kw shower
2. find current Power/voltage ie. 8000/230 =34 amps
3. Use next fuse size up from current...40amp fuse/breaker
4. select a size cable suitable to carry 40amps
5. Find length of run. ie 20 meters.
6. carry out volt drop calculation
design current (34amps) x Length of run (20 meters) x
millivolt drop per meter (7.83 mvolts/meter for 4 square
cable) >>> 34 x 20 x 0.00783 = 5.44 volt drop!
if volt drop exceeds 9.2 volts use bigger cable
Is This Answer Correct ? | 23 Yes | 5 No |
Answer / peer
If we know power calculate I(current) then select Breaker
and choose cable according to that.
Ex: Power is 50KW 3Ph supply.
I=100A (Apprx)
Breaker size for the above is 4c.35 sqmm+1c 16sqmm
E.C.C.
Is This Answer Correct ? | 20 Yes | 9 No |
Answer / vzvodator
See this program -
http://miroshko.kiev.ua/cablesel/wiresel_mini_en
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / iftekhar mahmud
Caterpillar generator produce (Two generators) 127*2=254 amp
at 11 kv .
What would be the cable size (XLPE) to supply 256 amp at 11
kv? Air or surrounding Temperature is 32 degree C. Cable
will go under ground at 2.5 feet depth. Group Rating Factors
is 3 cables. Clearance between cables is 7 cm. Soil
Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2
K.m/W
I would like to use 3 separate single core instead of using
3 core cable.
Some says I should use three separate single core 120RM cables.
Some says 70RM .some says 95.
I m totally confused.
Is there ant specific rule to determine cable size?
Ifte
My e mail address is ifte13@yahoo.com
Anyone please send me the answer to my e mail address,
i will be very glad.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / vijay shinde
it simple it should be select on how much current will
cable carry
Is This Answer Correct ? | 6 Yes | 13 No |
Answer / ahmed bilal
for calculating cable load, you have to email me
aoabilal@gmail.com
Is This Answer Correct ? | 4 Yes | 17 No |
Answer / ashutosh tiwari
according to kelvins economic choice of conductor size
formula is
total cost = (P1+p2*a)+p3*a
a>>>conductor size
Is This Answer Correct ? | 14 Yes | 30 No |
WHAT IS THE USE OF EARTH SWITCHES?
How star and delta connections inherently eliminate triplend harmonics?
low voltage means how much voltage? extra low voltage means how much voltage? medium voltage means hos much voltage? high voltage means how much voltage? Ex: low voltage - 1volt to 240volt like this
gd eve frndz my qstn is how convert sound energy to electrical energy
what is LT & HT?
Why r use in the tap changing x' mer.
What is the out put of a CT? How the ratio is decided ?
Definition of grid?
7 Answers L&T, Pace Power Systems, Vijai Electricals,
In a 3 phase system a neutral exists so that any unbalanced currents can flow through it towards earth.... but a phase demands a particular current as per the load attached to it....then where does the extra current come from the goes in the neutral??....I mean in an unbalanced system a phase demands a current as per its load attached....then where does the unbalanced current come from??
what will happen if i connect the buchholz relay in reverse direction.
what is green house effect?
what is the problem in manufacturing transformer with 0 degree phase displacement.???why alwasys go for DYn11 or DY5?Whys not DY0 i.e zero degree displacement between primary and secondary side vectors?