Answer / krishna rao vutukuru
when two transformers connected in parallel they share load based on their impedance.the transformer which have less percentage impedance will share more load.load on transformer is inversely proportional to % impedance
Is This Answer Correct ? | 5 Yes | 0 No |
Can I use measuring current transformers in protection purposes?
our scope called one core cable for distribution system so we like to use 4 core cable with one equipment grounding conductor so what kind of technical reasons i can say that the 4core is better then 1 core,
What is the name of the winding to which supply is given?
why can tv operate at low voltage??
why abcd parameters are called transmission parameters
What is a circuit breaker contact multiplier relay?
what are the analog quality input for protection function?what are minimum reqiments?
what will be the maximum winding temperature of 6.6kv HT motor 450kw, Full load current 49A. 50Hz Frequency.
Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)
Discribe type of fault in DOL and stardelta startor.
what is the function of commutator in dc motor?
What is the formula to find out the kvar required to improve the powerfactor from .85 to .99 at 1500kw, 415v.