how the percentage impedance affect the transformer
loading when connected in parallel.?
Answer / krishna rao vutukuru
when two transformers connected in parallel they share load based on their impedance.the transformer which have less percentage impedance will share more load.load on transformer is inversely proportional to % impedance
| Is This Answer Correct ? | 5 Yes | 0 No |
What happened If 3phase supply connected to slip ring side of slipring induction motor ?
what questions are asked in the interview for the post of an electrical maintenance engineer in FMCG companies?
why inuctive drop is not consider in DC MOTOR
if only one generator is running in droop mode parrallel with grid and suddenly grid breaker off what will happen? It will trip o/u freq or stay as it is? (urgent)
What is current and voltage?
what is encoder & its use?
is the secondary voltage of current transformer greater than primary voltage,,,,,,,,] give the example with ct burden,current ratio,and primary and secondary side voltage?
WHAT IS THE difference betwwen LT CABLE AND CONTROL CABLE
what is a pulse transformer? how rise time of pulse changes when ever the voltage changes?
I want single line diagram for AMF & DG syncronizing panel
what is the min and max ohmic resistance for the earthing rod installed for lighting poles for street light network
I have 150/1A Rating CT Suppose if i inject 15A in CT " Secondary" means what will happen ??????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)