how the percentage impedance affect the transformer
loading when connected in parallel.?
Answer / krishna rao vutukuru
when two transformers connected in parallel they share load based on their impedance.the transformer which have less percentage impedance will share more load.load on transformer is inversely proportional to % impedance
Is This Answer Correct ? | 5 Yes | 0 No |
What is the formula formula for Busbar sizing and what are the things to be consider for Busbar Calculation?
what is the function of a starter in a motor? explain RLC circuit.
What is the meaning, function and application of OLTC?
How much KVAr bank reqired for 630 KVA transformer on full load for maintain power factor upto.99
4 Answers Dhanalakshmi Industries, DLF,
How can I calculate the fault level of a transformer. 1. If fault is 3phase fault 2. If fault is 1phase fault 3. If fault is 2phase fault Dear all geniouses, can you help me by giving answer. If anybody want to send something then mail me at "msalam_shahin@yahoo.com"
why generator and t/f ratings given in kva?
what is the generation action and motoring action?
why we use to transmit the power in three phases intead of single phase ?
WHTA IS LIMT OF LEAKGE CURRENT OF 11 KV 1 CORE 1000SQ.MM. XLPE CABLE.LOAD ON CABLE IS AROUND 600AMP .LENGTH 500 MTRS.
Why do we use center tap transformer that used with portable tools
Why does the adjacent zone of protection overlap?
what is PDU in transformer?? which company manufacture??