Resistor switching is used in which type Circuit Breaker
?
a) oil filled CB b) Air blast CB c) Gas filled CB
Answers were Sorted based on User's Feedback
Answer / j.kesavan
oil circuite breaker only resistanceswitching.
| Is This Answer Correct ? | 36 Yes | 25 No |
Answer / sangram
Air Blast CB. High restriking voltage appears across the
contacts because of current chopping. If these voltages are
not allowed to discharge, they may cause break down of
insulation of the circuit breaker or the neighboring
equipment.
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / raul
ABCB.......during current chopping, capacitive current breaking.......high transient voltages r produced......resistance switching avoids dis by connecting a shunt resistance across d cb contacts.......
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / nikhil sharma
oil filled circuit breakers use resistor switching to
balance the voltage distribution amongst the contacts of
circuit breaker and to reduce the transient overvoltages
produced during arc inhibition process...
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / srinivas.k.p
b)Air blast c.b in that we reduce the re-striking voltage b\w the moving contact and fixed contact by using the resistance and allows the current though reverse leakage current will be avoided only we resistance used in air blast c.b other than we can't use in oil r gas..
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / anup $ingh
Obviously Air Blast Circuit Breaker
See.. http://www.oocities.org/hemant_thermal/airblastcircuitbreaker.htm
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / alpesh
can anybody tell me what is the use of that resistor switch???
| Is This Answer Correct ? | 2 Yes | 3 No |
what type of earthing is done on hilly rocks.
Find defination of KVA convert in to KW.
Why Trasformers rated in KVA
13 Answers College School Exams Tests, HAL, Oil and Gas Jobs,
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
why are the a.c.series motors preferred for electric traction
Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.
Require Generator Capcity ( KVA ) for 3 Phase Motor having 4.7Kw with starting current of 16amps?
Capacitor bank require for 1000amp load
2 Answers Biodeal, Pharmaceutical,
What is Grounding?
What is meant by Creepage Distance in Insulators?
What is superposition theorem?
I need to calculate the Battery bank back up for below configuration:- UPS - 120 KVA Battery Bank - 200Ah Volt of each cell - 12 V Total No of cell - 34 No's Can you please help me to get the battery back up time for above configuration...? along with formula
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)