Require Generator Capcity ( KVA ) for 3 Phase Motor having
4.7Kw with starting current of 16amps?
Answer / asif.k64@hotmail.com
KW=KVA*P.F
4.7=KVA*0.8
KVA= 6KVA approx
However the starting current is 16A hence we require a DG
of higher capacity.
This can be achieved by using a 7KVA DG.
| Is This Answer Correct ? | 5 Yes | 1 No |
Will u plz give me simple diagram for tube light connection & also function of chock?
8 Answers Bhushan Power Steel, Dalmia Group, Jindal, Practical Viva Questions, TCS, Windmoller,
single phase power supply give to separate one steel coup with water, what reaction create
why transformer does not obey ohms low?
what is floating charger and boosting charger?
why threre are two parallel lines in transformer's symbol?
how to ctrl motor by use of ac or dc drive.plz explain evdintly
what is the difference between elcb,rccb,mcb.
What is purpose of reactor?.What is different between line and bus reactor?
what is the Transmission line differential protection and why differential protection also have backup Line Distance Protection ?
for measuring current and etc.,why we use value of 1.732 in three phase calculation. not in single phase.why
What is the difference between expansion joints & thermal expansion joints in Bus bar
Why the substation measure in KV but not in the power ratings of transformer.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)