how many typetesting of transformers?
Answers were Sorted based on User's Feedback
Transfrmer has
1. routine tests
2. type test
3. special test
further type tests are
1. IR OF WINDINGS
2. POLARITY
3. VOL. RATIO
4. TEMP RISE TEST
5 DIELECTRIC LOSS
| Is This Answer Correct ? | 21 Yes | 5 No |
Answer / hitesh tiwari
1. IR VALUE TEST
2. MAGNETIC BALANCE TEST
3. MAGNETISING CURRENT TEST
4. VECTOR GROUP TEST
5. WINDING RESISTANCE TEST
6. OPEN CKT TEST
7. SHORT CKT TEST
8. TAN DELTA TEST
9. XMER OIL BDV TEST
| Is This Answer Correct ? | 7 Yes | 3 No |
1.insulation resistance test
2.ratio test
3.short circuit test
4.open circuit test
5.back to back test
6.oil testing
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / manoj patel
1) Ratio & tap continuity test
2) megger test
3) Magnetic balance test
4) vector group test
5) Inrush current mesurement test
6) Xmer oil BDV test
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / j.kesavan
dielectricbreakdowntest
acidneutralizationtest
sedimenttest
interfacial tensiontest
parts per million moisture test
colour and visual partical test
dissolved gas test
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / m.ravi
three types
1. o.c test
2. s.c test
3. back to back test
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / ksn murthy ,j.e,electrical
IR Values, Change of Siclikazal, any oil leakages, checking
of HT Lt side Insulator washers, Both Ht Side and lt side
cable terminations. Tx. Body Earth and as well Neutral earth
this is comes to transformer testing this is as per my
knowledge if any mistakes please excuse me.
| Is This Answer Correct ? | 0 Yes | 0 No |
FACP Means
Why transformer making sound during operations?
How to calculate busbar size & what is the procedure we make for determine that?
35 Answers Auko Tex, Integra, PowerTech, Shadhin Group,
how does calculate loss correction factor in transformer
How do you find HT and LT sides of a distribution transformer only by looking at it from outside?
What exactly is meant by harmonics and harmonic current?? and what is skewing with regard to this??
When we getting shock, its we getting from voltage or Current.
What is domestic transformer? Draw the connection of domestic transformer.
Why Ferranti effect not occurs at full load?
What is the function of neutral CT in transformer? Turn ratio of typical CT for 2MVA transformer ? or relation between full load current of transformer and neutral CT ?
1 Answers Electrical Inspectorate,
We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?
Could explain briefly of over excitation in transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)