I want to know which cable would be best to carry 125A current to a distance of 50m. Voltage is 3phase.
Kindly share the formula with answer.
Answer / sudesh
according to IEE regulations recommended voltage drop is 3%.
voltage drop=(400x3)/100
=12V
if we select 35sqmm pvc/xlpe/cu cable, it can carry 158A max.current.
so now we should consider about voltage drop of cable.
true voltage drop=volt.drop for cable*Current*Distance
=1.15mV/A/m * 125A * 50m
=7.18V
7.18 < 12
so 35sqmm cable would be best to carry 125A current.
| Is This Answer Correct ? | 2 Yes | 0 No |
Why transformer rating is represent in KVA?
7 Answers Bhel, Sonalika, Usha Martin, Wipro,
WHY HOLDING CONTACTOR OF MOTOR STARTER IS CALLED NO VOLT COIL.
Re: What do you mean by Power factor of a generator? Power factor purely depends on the load (wether inductive, reactive or unity) then what does the Power factor mentioned on the generator nameplate means?
my question is that....few days ago i had installed a three phase motor starter for an electric saw.the motor will run and make the hydraulic pressure which will be goes to pressure cylender by up and down lever.two number of limitswitches are also installed on cylinder for safety of motor.now when the arm of cylinder reaches to the upper or lower limit it will cut the motor's line.and motor will be stop.now wana know that what will i do that motor runs continue after the limitswitch cut it down but it shold not be made any pressure.pls answer me in brief.
At the starting of dc motor and syn.motor and induction motor high current flowing through the winding. Due to this the windings burnt out. To avoid this different types of starters are used. But incase of transformer what Will be used (At starting no emf is induced in the primary winding)?
what is meant by vector group of a transformer? How can it be derived?
please anybody help me to find out the BHEL trainee Exam previous year questions papers . if u ve pls. send it to surekhared@gmail.com
Neutral CT for 45MVA 132/11 KV YNd11 Transformer. NCT REF CLASS-PS or 5P20 with 20VA burden which is suitable.
if receiving voltage is higher than sending ones what will be the effect of receiver
Is itnecessary to use capacitor in an Fluorescent Tube Light Fixtures? Why? What if not capacitors are not included?
in single phase circuit if i connect a heater between phase and neutral, then what will be the current path? phase to neutral or neutral to phase.
How to know vacuum in vacuum cylinder of breaker in working condition
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)