since the losses in the transformer is iron and copper loss
which depend upon the voltage and current but not on the
angle between them
Is This Answer Correct ? | 25 Yes | 1 No |
Answer / veerendra
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
Is This Answer Correct ? | 18 Yes | 1 No |
Answer / sangayya s k
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / okereke okorie daniel
Transformer is rated in kva because the efficiency of a
transformer depends on the copper losses annd the iron
losses which are voltage and current respectively, hence
the rating in kva.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / padmaja
The x'mer rating is in kva because as the iron losses in
x'mer is depends on voltage i.e. as per o.c. test carried
out on x'mer & copper losses is depends on current i.e. as
per s.c. test carried out on transformer.
so depending on the losses reflects voltage & current unit.
hence the rating is explained in KVA to give a detail how
much amount of power it can transfer.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sangayya sk
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rsundareee
The transfor rating is in kva because as the iron losse
depending on the voltage and copper loss depending on the
current,so total loss depending on the voltage and current
so it,s called kva.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m.gopinath
All ac machines rating is mentioned in kva on name plates
where as dc machines rating is mentioned in kw. In the case
of dc, there is no question of pf as the loads for dc are
always resistive in nature and the pf is always unity. But
in the load can be resistive, inductive or capacitive in
nature in case of ac machines.
Let us calculate current for different loads (ie for
different pfs) in case of ac machines if their rating is
mentioned in kw:
16 MW (not in MVA as in normal case), 132/33 KV T/F
Case 1: For resistive load
HV Current = 16000/(1.732*132*1)= 70 A (approx.)
Case 2 : For inducive/capacitive load at 0.8 pf
HV Current = 16000/(1.732*132*0.8)= 87.5 A (approx.)
observe the above two cases, for a given rating in MW(16 MW)
the current is quiet different and it will depend on the
nature of the load on T/F. This is not in the case of DC as
the nature of load is always resistive.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / uddin
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
Is This Answer Correct ? | 7 Yes | 8 No |
Answer / varun
i m not sure but i thik due to p.f. beacause p.f different
at all time.
Is This Answer Correct ? | 0 Yes | 5 No |
Can anyone explain how the vector diagram of a transformer which doesn't have name plate be found whether it is Dy11/Dy5/Yd11 and so on?
i have need all detail above basic transformer question..
what is the transformer
What is rms value wher it is used??????????
Hello seniors m an engineering student in 3rd yr..i want to know what are the software course in electrical field?i wanted to do certification course but i dont know much about the course?..Regards
What is difference between isolator and circuit breaker?
what use can we make of 3rd harmonic component
5 Answers Bhel, General Motors GM,
a power supply to be constructed from voltage cells is required to provide Max. 20A Current with a terminal voltage of 6v.Several voltage cells are available each of which has terminal voltage of 1.5V & each of which can supply a max current of 5A .the no of cells required will be ??
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
1.wat is the advantage of induction motor? 2.wat is diffrence between 1-phase and 3-phase induction motor?
what is the speed of mixie?
how to calculate the capacity of CT operated LT trivector meters on a particular distribution transformer.