Answer / siva
since the losses in the transformer is iron and copper loss
which depend upon the voltage and current but not on the
angle between them
| Is This Answer Correct ? | 25 Yes | 1 No |
Answer / veerendra
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / sangayya s k
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / okereke okorie daniel
Transformer is rated in kva because the efficiency of a
transformer depends on the copper losses annd the iron
losses which are voltage and current respectively, hence
the rating in kva.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / padmaja
The x'mer rating is in kva because as the iron losses in
x'mer is depends on voltage i.e. as per o.c. test carried
out on x'mer & copper losses is depends on current i.e. as
per s.c. test carried out on transformer.
so depending on the losses reflects voltage & current unit.
hence the rating is explained in KVA to give a detail how
much amount of power it can transfer.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sangayya sk
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rsundareee
The transfor rating is in kva because as the iron losse
depending on the voltage and copper loss depending on the
current,so total loss depending on the voltage and current
so it,s called kva.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m.gopinath
All ac machines rating is mentioned in kva on name plates
where as dc machines rating is mentioned in kw. In the case
of dc, there is no question of pf as the loads for dc are
always resistive in nature and the pf is always unity. But
in the load can be resistive, inductive or capacitive in
nature in case of ac machines.
Let us calculate current for different loads (ie for
different pfs) in case of ac machines if their rating is
mentioned in kw:
16 MW (not in MVA as in normal case), 132/33 KV T/F
Case 1: For resistive load
HV Current = 16000/(1.732*132*1)= 70 A (approx.)
Case 2 : For inducive/capacitive load at 0.8 pf
HV Current = 16000/(1.732*132*0.8)= 87.5 A (approx.)
observe the above two cases, for a given rating in MW(16 MW)
the current is quiet different and it will depend on the
nature of the load on T/F. This is not in the case of DC as
the nature of load is always resistive.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / uddin
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / varun
i m not sure but i thik due to p.f. beacause p.f different
at all time.
| Is This Answer Correct ? | 0 Yes | 5 No |
why the efficiency of the dc machine is high ,when it is operated as a generator?
what is the size of cable for 15kw motor and 85 meter cable length using with vfd
how we calculate full load current of A.C & D.C Motors?
List advantges of active filter over passive filter?
what is the power factor of an inductive load ? (i) Zero (ii) Lagging (iii) Leading (iv) Unity
What is the following which is printed on electrical appratuses like AC21 ,AC 23 , etc ?
Can i connect all earth pits in ring system..., And wat IS 3043 says...please help me
What's the differs between voltage & current & emf.
WHY CAN WE NOT CHAGE SPEED OF SYNCHRONOUS MOTOR...............................JUSTIFY
ACCORDING TO IEC WHAT SHOULD BE THE MINIMUM HEIGHT OF G.I. STRUCTURE OF CT, PT, ISOLATOR, LA?
Which standard we are following earthing resistance test
why the transformer primary and secondary windins vector groups vary? why it is something like Dy11 and not as Dy or Yy...
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)