What is Isolation Transformer???
Answers were Sorted based on User's Feedback
Answer / thowsif_emerson_csm team
Isolation transformer means that no direct electrical
connection exists between source and load. But that's true
for any transformer (other than an autotransformer). What
makes the drive isolation transformer different is the
placement of grounded electrostatic (Faraday) shielding
between and around primary and secondary windings. That
provides up to a million-fold decrease in the capacitive
coupling involved in transferring common-mode voltage
disturbance. Without such shielding, that capacitance
allows passage through the transformer of high-
frequency "noise" and transient voltage spikes.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / jaggu
for isolating DC while permitting the flow of AC between two circuits for isolating one ckt frm the other.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / phani
An Isolating t/f is one in which the primary and secondary winding turns ratio is 1:1 . so it does not either steps up or steps down the voltage levels but it just isolates the source and load connected to the transformer. I think we cannot find an isolating transformer in practice.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / patelsheleph
An isolation transformer does not have a direct electrical
path from the power input side to the power output side. The
term is also used to define how much electrical isolation
exists between the input and output windings. For example
when using line-voltage input transformers to power low
volatge device handled by humans, a high degree of isolation
is required for safety.
Isolated transformers often use separate bobbins for the
primary and secondary coil windings, but usually the
windings are just wound on top of each other with insulation
in between.
Non-Isolated transformers are becoming rare. A common
example is the "Variac" which is a non-isolated variable
transformer. Usually the term "auto-transformer" is used to
describe non-isolated transformers. They are rarely found in
consumer products.
Although any transformer with a separate primary and
secondary winding is an isolation transformer to some
extent, The term is usually used to denote a special-purpose
transformer built just for that use. It is tested and rated
to withstand a very high voltage difference, called the
withstand voltage, so that even if thousands of volts are
applied to the primary, it will not leak through to the
protected side. These transformers are used in the medical
industry, to protect patients hooked up to monitoring
instruments that are powered by utility mains, as well as
other uses.
Is This Answer Correct ? | 4 Yes | 3 No |
For single phase(phase to neutral) having potential difference 230.in three phase(phase to phase)we have 440V HOW...?
Why we are measured insulation resistance applied through DC Voltage?
whu the transformer noise during running condition?
why weight is put on pulley?
what is the circulate the diesel in DG in side pls tell parts name and picture with circulate the diesel
While DG is on Load? we can start the capacitor bank?
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
Dear sir,We have a 7.5hp motor,it was running smoothly and suddenly one winding is carring more current then others(r=6.5,y=6.3,b=10)..whts wrong with tis...?
what is difference between Motorised MCCB & ordinary MCCB?
what is load which is indicated in power plant generation panel? in any power plant
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The rated current is 26Amps. Application is for the blower. The motor takes ( no load without coupling impller ) only 2.5A and 5Amps in star & delta starter test.Need to know why its taking high current.