Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?

Answers were Sorted based on User's Feedback



what is the CT of protection and CT of metering ? what is class 5P10 & 5P20 and class PS ?..

Answer / siva

Two type of core in ct,
1,protection core
2,metering core
protection core; only for protect the equipment used to
relay based.

metering core : this is only for showing the current in
ammeter .

In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-accuracy class.
p- protection
10-10% error.
20-20% error.

protection class:it is calculated by the knee point voltage
test.

Is This Answer Correct ?    6 Yes 18 No

what is the CT of protection and CT of metering ? what is class 5P10 & 5P20 and class PS ?..

Answer / kiran

CT for protection means for protecting other equipment in
the ckt. based on the protection class ex:5P10
5 - % of accuracy
P - for protection
10- 10% of rated current also it withstood
CT ratio 300/1A 10% of rated value means it can withstand
upto 3000A if any abnormal condition.

Normally for metering we use CL:1 , 0.5 ,0.2 because for
metering accurate value we need.

econamy purpose we won't use 1P10 or 0.5P10 and also
protection we don't want that much accuracy.

Class PS : based on knee point voltage we caliculate PS.
this is for special purpose.

Is This Answer Correct ?    13 Yes 26 No

what is the CT of protection and CT of metering ? what is class 5P10 & 5P20 and class PS ?..

Answer / saravanan

Two type of core in ct,
1,protection core
2,metering core
protection core; only for protect the equipment used to
relay based.

metering core : this is only for showing the current in
ammeter .

In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-accuracy class.
p- protection
10-10% error.
20-20% error.

protection class:it is calculated by the knee point voltage
test.

Is This Answer Correct ?    15 Yes 59 No

what is the CT of protection and CT of metering ? what is class 5P10 & 5P20 and class PS ?..

Answer / arunmozhi

there are two type of ct in field,
1,protection CT
2,metering CT
protection CT; only for protect the equipment used to
relay based.

metering CT : this is only for showing the current in
ammeter .

In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-acurancy class.
p- protection
10-10% error.
20-20% error.

ps class:it is calculate to the knee point voltage.

Is This Answer Correct ?    20 Yes 74 No

what is the CT of protection and CT of metering ? what is class 5P10 & 5P20 and class PS ?..

Answer / anil konkimalla

Protection CT doesnt need much accuracy and it should not
saturate in fault condition. PS class means protection
class CT. 5P10 means 5% is the maximum composite error
shown while 20 times fault current flows.Hence 5P10 is
superior comparing to 5P20

Is This Answer Correct ?    63 Yes 122 No

what is the CT of protection and CT of metering ? what is class 5P10 & 5P20 and class PS ?..

Answer / syed naveed akhter

ct can use as protuction in supply lines where 3 phase use
in different areas saperatly for example in lighting in
hall, if current pass throw one phase high then ct detect
emf out side the wite and generate some supply to cut the
main source.

as you know that ct is current transformer, it fix around
the wire where current flow. when load take some current
then out side of wite some emf produce which detect by ct
and its pass some voltage which use to measure (it is a
calculation which i dont know) help to metering.

Is This Answer Correct ?    8 Yes 68 No

Post New Answer

More Electrical Engineering Interview Questions

Is it possible to connect a safety device in to parallel?

0 Answers   Jones Lang LaSalle,


why two contacts(in series) are using in closing circuit

3 Answers  


What is the function of an Auto reclosure relay. How does it work??

4 Answers   KSEB,


How could I get a certificate of competency as Electrical Supervisor? I have completed By BTech in Electrical this year(2012) for VJTI Mumbai Maharashtra. Is it compulsory to be produced while joining?

0 Answers   ONGC,


What is the use device of the grid.

1 Answers   Premier,


i asked a funny question in Electrical ohms law V=IR in const temp voltage is directly proportional to current Power p=VI cos@ in that formula Voltage is indirectly proportional to current Try to give me the fact what is happening in Electrical.. contact Thanigai_1984@yahoo.co.in

3 Answers  


A parallel flow heat exchanger will perform better than a counter flow heat exchanger. State if the statement is true or false.

0 Answers   Blue Star,


Sir, I m 3rd year student 4m DCE and want to do internship in siemens or l&t or any other mnc related to electrical engineering. please tell me the procedure 4 same and oblige me

0 Answers  


why impedance test in power cables?

1 Answers   CSE,


for a 11kv transmission line what capacity of CTs & PTs are required?

4 Answers  


whats the one main difference between UPS & inverter ? And electrical engineering & electronics engineering ?

16 Answers  


we r having 3 core 3 1/2, 4 core cables how we can know this cable has to be used for this purpose?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)