Answer / siva
Two type of core in ct,
1,protection core
2,metering core
protection core; only for protect the equipment used to
relay based.
metering core : this is only for showing the current in
ammeter .
In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-accuracy class.
p- protection
10-10% error.
20-20% error.
protection class:it is calculated by the knee point voltage
test.
Is This Answer Correct ? | 6 Yes | 18 No |
Answer / kiran
CT for protection means for protecting other equipment in
the ckt. based on the protection class ex:5P10
5 - % of accuracy
P - for protection
10- 10% of rated current also it withstood
CT ratio 300/1A 10% of rated value means it can withstand
upto 3000A if any abnormal condition.
Normally for metering we use CL:1 , 0.5 ,0.2 because for
metering accurate value we need.
econamy purpose we won't use 1P10 or 0.5P10 and also
protection we don't want that much accuracy.
Class PS : based on knee point voltage we caliculate PS.
this is for special purpose.
Is This Answer Correct ? | 13 Yes | 26 No |
Answer / saravanan
Two type of core in ct,
1,protection core
2,metering core
protection core; only for protect the equipment used to
relay based.
metering core : this is only for showing the current in
ammeter .
In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-accuracy class.
p- protection
10-10% error.
20-20% error.
protection class:it is calculated by the knee point voltage
test.
Is This Answer Correct ? | 15 Yes | 59 No |
Answer / arunmozhi
there are two type of ct in field,
1,protection CT
2,metering CT
protection CT; only for protect the equipment used to
relay based.
metering CT : this is only for showing the current in
ammeter .
In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-acurancy class.
p- protection
10-10% error.
20-20% error.
ps class:it is calculate to the knee point voltage.
Is This Answer Correct ? | 20 Yes | 74 No |
Answer / anil konkimalla
Protection CT doesnt need much accuracy and it should not
saturate in fault condition. PS class means protection
class CT. 5P10 means 5% is the maximum composite error
shown while 20 times fault current flows.Hence 5P10 is
superior comparing to 5P20
Is This Answer Correct ? | 63 Yes | 122 No |
Answer / syed naveed akhter
ct can use as protuction in supply lines where 3 phase use
in different areas saperatly for example in lighting in
hall, if current pass throw one phase high then ct detect
emf out side the wite and generate some supply to cut the
main source.
as you know that ct is current transformer, it fix around
the wire where current flow. when load take some current
then out side of wite some emf produce which detect by ct
and its pass some voltage which use to measure (it is a
calculation which i dont know) help to metering.
Is This Answer Correct ? | 8 Yes | 68 No |
what are the energy savings methods that are existing in coal based power plant?
what is Wave Trap? And its Function ? Detail? Where it is Used?
Why we use Carbon & graphite mixxed brushes in the DC motor?
Why distribution transformer secondary voltage is 0.433kV instead of 0.415kV.all other switchgear rating are 415 volt??
What is working of Trip Ckt.Supervision Relay?
Best way to measure the Soil resistance of rocky soil, three probe method and four probe method
How Load Factor, Demand Factor, Diversity Factor etc best applied in designing an electrical circuit? Is it allowed to consider these factors in each and every panel in an electrical distribution system? Can any body suggest a good book for reference?
How to calculate KW what is the formula for KW.
Define Current Transformer? Working & TYpe's Of C.T.
What is working Priniciple of TVSS ????
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
what is oti and wti