what is the CT of protection and CT of metering ? what is
class 5P10 & 5P20 and class PS ?
Answer Posted / saravanan
Two type of core in ct,
1,protection core
2,metering core
protection core; only for protect the equipment used to
relay based.
metering core : this is only for showing the current in
ammeter .
In different type of class in CT 5p10,5p20 And ps it is
used for protection purpose only ,
5-accuracy class.
p- protection
10-10% error.
20-20% error.
protection class:it is calculated by the knee point voltage
test.
| Is This Answer Correct ? | 15 Yes | 59 No |
Post New Answer View All Answers
what is the solution for meger test failed the MV cable?
TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2
Please explain the following and how these are working with PLC unit 1.I/O Module 2.I/O Device 3.Adaptor Card 4.Ribbon Adaptor 5.RS 485-FC
area control error
What is FM200 Gas??Applications........
What is the difference between amorphous core transformer and CRGO core transformer?.
Why 1/3 is used in symmetrical components?
plz tel me syllabus and exam date 4 jr executive engg (electrical)
What is the difference between resistance grounding system and resistance earthing system?
State kirchoff current law?
What is rotating magnetic field?Discuss elaborately.
how to calculate earth fault relay current and CBCT ratio
What is gross error?
what is mppt (maximum power point tracking ) and how they used in solar power generation ??? what are the main components used in mppt?????
Proviiding the Dedicated N earth and individual Body Earths ,Finally these all looped /Now my Question :- will it not harm in case of Transformer Fault current flows in Dediacted N Earthing to Looped Body Earthing.