how to calculate circuit breaker capacity
Answers were Sorted based on User's Feedback
Answer / hari
If u have the fault mva and the voltage level at which the
CB is to be installed then :
Normal current would be the continuous current flowing in
the line ( u can take the next higher value from standard
values to take care of over current)
Breaking capacity would be tha fault MVA.
Rated symmetrical breaking current in kA would be Fault
MVA*1000/(1.732x Voltage in kV)
Rated making ct would be peak value of symmetrical breaking
current i.e 2.55 times breaking current
Short time rating would be rated symm breaking ct for 3 secs
| Is This Answer Correct ? | 95 Yes | 17 No |
Answer / ravi kumar singh
Breaking capacity will be always iN MVA= 1.732*Voltage in KV * cerrent in KA
making capacity = 2.55 * symmetrical breaking capacity
note:-( 1.41*1.8=2.55)
full load current= 1.8 * KVA
ravi kumar singh
| Is This Answer Correct ? | 51 Yes | 10 No |
Answer / nighot jagdish
Rated symmetrical breaking current in kA would be Fault
MVA*1000/(1.732x Voltage in kV
| Is This Answer Correct ? | 50 Yes | 19 No |
Answer / karthik
BREAKING CAPACITY OF CIRCUIT BREAKER
=SQRT(3) x V x I x 10-6
V is supply voltage
I is circuit breaker capacity
answer appears in MVA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / usama badran ali
el salamo aleekom
to calculate circuit breaker breaker capacity...there are
four steps :
1-indicate all actual nominal voltages and MVA of your
system
2-indicate the location of circuit breaker.
3-calculate the actual impedance between the known supply
to the point of fault at which near to circuit breaker.
4-then calculate:
a- short circuit current =
voltage of supply/((3^0.5)actual impedance)
b-MVA short citcuit=
(3^0.5)*voltage of supply*short circuit current
c c-breaking capacity=
MVA short citcuit*assymetry factor.
or
short circuit current*assymetry factor
notes:
Assymetry factor:1.5~1.6 for midium voltage
1.25 for low voltage
MVAshort circuit= fault level
breaking capacity: it is the value of peak current where
the circuit breaker is breaking.
| Is This Answer Correct ? | 8 Yes | 11 No |
we can consider circuit breaker capacity for particular
feeder depend upon the 1.2 times of full load current for
receiving end equipments
| Is This Answer Correct ? | 4 Yes | 12 No |
Is itnecessary to use capacitor in an Fluorescent Tube Light Fixtures? Why? What if not capacitors are not included?
Stator of three phase induction motor creates Rotating Magnetic field.But why not Transformer?
use of choke in APFC panels
if the rotor of induction motor is purely inductive then what is the electromagnatic torque.........
AC 230V BULB GIVING DC SUPPLY WHAT HAPPENS?
How would your past experience translate into success in this job?
I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.
why we r used APFC Panel in industrial area.when P.F. low then wat will be the effect in our system?
10 Answers ABB, Georgio Rocks, Piramal Healthcare, Zenith Engineering Corporation,
i m in need of current rating chart of heavy duty pvc/xlpe, cu/al cables. can somebody provide me? if yes, plz send me at ashish_patel111@yahoo.com
what is open star connection or open delta.
What are the Return ( Monthly / quarterly/ Annual submitted to Electical Inspector for an establishment (Factory in Maharashtra-- Small scale category having seperate HT line of 22KV ) as per Maharashtra Electricity Act
why there is spacing between two rails in railway?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)