What it indicates by 25/41MVA on transformer?
Answers were Sorted based on User's Feedback
The transformer Full load Capacity is 41 MVA.
Then why 25/41 MVA, Its type of Cooling, UPto 25 MVA one
type of coling, & 25-41MVA another type of cooling.
For example: Upto 25MVA -ONAN(oil natural & air natural)
cooling
&above 25- 41MVA-ONAF(oil natural & air forced)
cooling.
| Is This Answer Correct ? | 27 Yes | 2 No |
Answer / t eswara rao
25 / 41 MVA rating means that
25MVA rating with normal cooling arrangement.
41MVA rating with special cooling arrangement, like External
cooling fan arrangement for more cooling
For ex: 25MVA with ONAN (Oil Natural & Air Natural)
41MVA with ONAF (Oil Natural & Air Forced)
| Is This Answer Correct ? | 21 Yes | 0 No |
Answer no#2 Are u crazy, where will you represent the
voltage in MVA?
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / akshay deep tripathi
25 mva is the primary windig voltage and 41 mva is the
seconry winding voltagr of a transfarmer
| Is This Answer Correct ? | 3 Yes | 47 No |
What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???
In LT cables 3.5 core cable are available that means 3 core and .5 for neutral Why .5 for neutral and is there any reason for that please suggest thanks and regards pavan kumar
how can we measure 220kv or more than these voltages ...?and also how can we conform whether we r getting 220kv from generating stations throuth the h v transmission lines?
What is the difference between MCCB,ELCB,RCB & MCB
what type of insulation is used for over head lines?
can we ran equipment up to 10kw between phase to grounding/ earthing. beside above can we use grounding instead of neutral. .
1 Answers TNEB Tamil Nadu Electricity Board,
What is the basic principle of circuit breaker?.. I read that it works on electro-mechanical principle... Does it require both electric n magnetic conversion to act?
differance b|w ground, neutral&earth
If we impress a dc voltage of 230 V on an unloaded 230 V, 50 Hz transformer it wi A give high secondary voltage B burn out C give secondary voltage as per K D none of these
can i connect wavetrap in 2 different phase in EHV line?
how to calculate efficiency of voltage and current controlled welding transformer?
On a transformer name plate %IZ(%Impedence) is mentioned. What is the meaning of %IZ and how it is calculated?
3 Answers Ambe Consultancy, Siemens,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)