What it indicates by 25/41MVA on transformer?
Answers were Sorted based on User's Feedback
The transformer Full load Capacity is 41 MVA.
Then why 25/41 MVA, Its type of Cooling, UPto 25 MVA one
type of coling, & 25-41MVA another type of cooling.
For example: Upto 25MVA -ONAN(oil natural & air natural)
cooling
&above 25- 41MVA-ONAF(oil natural & air forced)
cooling.
| Is This Answer Correct ? | 27 Yes | 2 No |
Answer / t eswara rao
25 / 41 MVA rating means that
25MVA rating with normal cooling arrangement.
41MVA rating with special cooling arrangement, like External
cooling fan arrangement for more cooling
For ex: 25MVA with ONAN (Oil Natural & Air Natural)
41MVA with ONAF (Oil Natural & Air Forced)
| Is This Answer Correct ? | 21 Yes | 0 No |
Answer no#2 Are u crazy, where will you represent the
voltage in MVA?
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / akshay deep tripathi
25 mva is the primary windig voltage and 41 mva is the
seconry winding voltagr of a transfarmer
| Is This Answer Correct ? | 3 Yes | 47 No |
how to improve power factor correction?
i am venkat i got gre 930(verbal 270 quanta 660) and my toefl score 105..here question is why u got less score in gre ? what i supposed to tell...any chance of rejection is there...my accadamics record is very good
difrence bitwin boost charge and float chargeing
how to identified power tranfer line is how much KV????
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
PLZ SEND ME SOME UNIQUE PROJECT OF ELECTRICAL ENG (B.TECH)
What is the difference between air & vaccum circuit breakers?
which oil used in transformer?
WHAT IS THE TECHNICAL SPECIFICATION OF C CURVE & D CURVE LEGRAND MAKE MCB
Sir, Please tell me that how I will calculate the efficiency of rectifier. Because input is ac and output is dc. Is it right to put two unlike signal together.
my 10 hp submersible pump is tripping when connected through ELCB.I have checked the megger value of the coil's with body.It was found to be 0.2mega ohm.that is leakage is there.But when connected to mccb it is not tripping.no leakage current in the motor.Is it safe to connect to mccb? what are the problem's will arise if future?also tell me in ELCB no neutral is connected to motor.than how ELCB was working?
what are the condition that makes hooter blow?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)