Answer / nimish
It is an inverse definite minumum time relay. In IDMT relay
its operating is inversely proportional to fault current
and also a characteristic of minumum time after which this
relay definately operates.
| Is This Answer Correct ? | 250 Yes | 22 No |
Answer / klm
It is inverse in the sense , the tripping time will decrease as the magnitude of fault current increase.
simply saying,
"for a fault current of 25KA-the time delay may be 2s.
& for a fault current of 30KA the tme delay may be 1.5s.thus as the fault current increases the time delay decreases.
| Is This Answer Correct ? | 163 Yes | 6 No |
Answer / suthan prabhu
It is Inverse Definite Minimum Time Relay. This will work
inversly proportional to Fault current and our time delay
settings in the relay.
| Is This Answer Correct ? | 84 Yes | 20 No |
Answer / prasanna
IDMT - Inverse Definite Minimum Time lag
Inverse - Operating time is inverse with fault current magnitude
Definite - Time characteristics is definite (Near constant) irrespective of current magnitude
Minimum time lag - time taken to operate is less when compared to other protection relays
| Is This Answer Correct ? | 52 Yes | 8 No |
Answer / md.moazzem hosen
IDMT relay means inverse definite minimum time relay.That
means when fault current increases then operating time
decreases.
| Is This Answer Correct ? | 41 Yes | 7 No |
Answer / er. mohammed yusuf fahad
The IDMT Inverse definite minimum time relay is one such
type of relay where the delay time of the relay is
inversely proportional to the magnitude of the fault
current. For ex. If the fault current is of the magnitude
of 8KA the delay taken by the relay to tripp the ckt may be
3 sec likewise if a fault current of 16KA persists in the
system the IDMT delay time will automatically reduce to 1.5
sec and so on. It is used in applications of overcurrent
relays and earth fault relays.
| Is This Answer Correct ? | 22 Yes | 0 No |
Answer / shyam
it is a type of inverse current relay but with minimum time
delay
| Is This Answer Correct ? | 37 Yes | 16 No |
Answer / adesh
is an inverse definite minimum time relay
there are 2 precautions to be considered when using this these precautions are the time setting and the current tap setting
these are to be considered since the relay is dependent on the inverse of time
| Is This Answer Correct ? | 22 Yes | 5 No |
Answer / n.ravi teja
it is inverse definite time relay.and in the name it self
inverse means when fault current is more then its operating
time is less.because if it takes more time the equipment
may damage.so to avoid this the relay is made with inverse
characteristics.
| Is This Answer Correct ? | 12 Yes | 4 No |
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
What is the difference between Class PX & Class X CT's
please send 5yearje solved papers on my email himmatsinghnathawat@gmail.com
the voltage per turn of a primary winding of a transformer is the same as the voltage per turn of the secondary winding of the transformer. why?
What is the comparison between 30mA DP RCCB and 100mA DP RCCB and can replace it against 63A MCB
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
How do we calculate Blower drive Power (kw) If we have Volume m3 and Pressre (mmWC)
why ac can not be stored?
Brief difference btween aluminium & copper conductor
for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???
will three phase energy meter run without one phase
WHAT AC (HI VOLTAGE TEST) VOLTAGE SHOULD APPLY FOR 33KV CABLES.EXPLAIN IN DETAIL
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)