1.what is the difference between MPCB and MCB ?
2.what is the difference between MPCB and MCCB ?
Answers were Sorted based on User's Feedback
Answer / george m s kingsley
Hai dear engineers,
MPCB- Motor Protection Circuit Breaker
It breaks the circuit depend upon the properties of the machine.
eg:- Set the breaking current of 10Amps in MPCB for the
Machine rating of 10Amps.
So that the machine take the starting current of 1.3 to 1.5
times from the rated.MPCB does not react here. But if the
current goes 120% to 150% based on time duration it breaks
the circuit.(overload relay supportive to machine)
MCB- Miniature Circuit Breaker.
It doesn't bother about Machine. If the Ampere goes more
than the MCB range it breaks the circuit.
Short circuit protection
(overload relay supportive to resistive, lighting load,
control circuit etc.)
Is This Answer Correct ? | 54 Yes | 10 No |
Answer / saroj kanta nayak
1.Both MCB and MPCB protects against Short circuit and Over load. But MPCB is better for the more starting current taken by Motor. and the Current range can be ardjusted. In mcb we cannot ardjust the current.
2.Both MPCB and MCB protects against Short circuit and over load. But the main difference is MCCB have NO & NC contact built in which used for the control circuit. untill and unless MCCB made on control circuit cannot made on(for motor starter feeder) In camparision to MCB, MCCB have higher current rating. And if current rating increases ACB(air circuit breakers used).
So in conclusion All MCB,MCCB & MPCB gives the same protection even can be used in any others place. But MPCB is best for MOTOR protection as it have Inbuilt OVER LOAD RELAY and current range can be selected. Others(MCB&MCCB) may give trouble of unnecessary tripping during starting of motors.For short circuit protection all devices like MCB,MCCB&MPCB functions similar way.
Saroj kanta Nayak
SIEMENS LTD.
KALWA,MUMBAI
Masters In technology from
Nation Institute of technology, Silchar.
Is This Answer Correct ? | 30 Yes | 2 No |
Answer / chetan
MPCB-MOTOR PROTECTION CIRCUIT BREAKER
MCB-MINIATURE CIRCUIT BREAKER
MPCB TOTALY DIFFERENT FROM MCB AS IT IS NOT ONLY SIMPLE
CIRCUIT BREAKER AS MCB IT HAS INBUILT OVERLOAD RELAY RANGE
IF THE LOAD ON THE MOTOR EXCEEDS ITS CURRENT ABOVE THE
LIMIT OF MPCB IT TRIPS.
MCCB-MOULDED CAGE CIRCUIT BREAKER
MCCB IS A CIRCUIT BREAKER HAVING HAIGH LOAD CAPACITY THAT
IS ABOVE 63 AMPERE WE ARE GENERALY USE MCCB INSTED OF MCB
Is This Answer Correct ? | 15 Yes | 7 No |
Answer / rohan
MCB(Miniature Circuit Breaker) which ranges from 0.5A to
63A, but now HRC MCB has rating upto 125A, anything higher
than this rating requires a design which can handle so high
current so MCCB(Moulded Case Ciruit Breaker) which has raing
upto 1000A, whereas, MPCB is used for Motor Protection Device.
Is This Answer Correct ? | 9 Yes | 6 No |
Answer / amu
Dear George M S Kingsley
plz tell me what is the diff b/w lugs and thimbles in electrical field.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rajesh
MPCB means motor protection circuit breaker.its called
manual motor starter.its not a motor its also protective
eqiupment.its working range is 0.1A-25A.MCB(miniature
circuit breaker)and MCCB(molded case circuit breaker)
working range is from the above 10A.
Is This Answer Correct ? | 9 Yes | 18 No |
How to calculate VCB rating for 33KV ,25 MW Power line?
Is it possible to download the Siemens Selection Chart(TYPE 2 coordination) for 1) fuseless selection 2)Fuse selection
Yazaki india pvt ltd interview questions qurey related
Based on what the rating of machines are provided??(ANswer should in single word)
19 Answers Asian Paints, Bhel,
How earth resistance reduses by pouring water coal and salt?
What is state space method ? Why its used ? Can it applicable on linear, non-linear, 1st order, higher order, homogeneous, non-homogeneous, open-loop , closed loops , stable & unstable systems ?
WHAT IS RMU & HOW IT WORK,IT USEFUL FOR HT OT LT POWER DISTRIBUTION MAUFACTUERE IN INDIA.
What is rated value? is it phase values or line values?
why in transformers voltage given is in the multiple of 11
Why PT voltages are measured with respect to ground? What do u mean by voltage or current polarized.
Draw the single line diagram of the power station?
Hello,l am complete dip and i was working maintance in ht dep again i study b.e completed again one year exp in ht totally two year i am ealigble in c license