1.what is the difference between MPCB and MCB ?
2.what is the difference between MPCB and MCCB ?
Answers were Sorted based on User's Feedback
Answer / george m s kingsley
Hai dear engineers,
MPCB- Motor Protection Circuit Breaker
It breaks the circuit depend upon the properties of the machine.
eg:- Set the breaking current of 10Amps in MPCB for the
Machine rating of 10Amps.
So that the machine take the starting current of 1.3 to 1.5
times from the rated.MPCB does not react here. But if the
current goes 120% to 150% based on time duration it breaks
the circuit.(overload relay supportive to machine)
MCB- Miniature Circuit Breaker.
It doesn't bother about Machine. If the Ampere goes more
than the MCB range it breaks the circuit.
Short circuit protection
(overload relay supportive to resistive, lighting load,
control circuit etc.)
| Is This Answer Correct ? | 55 Yes | 10 No |
Answer / saroj kanta nayak
1.Both MCB and MPCB protects against Short circuit and Over load. But MPCB is better for the more starting current taken by Motor. and the Current range can be ardjusted. In mcb we cannot ardjust the current.
2.Both MPCB and MCB protects against Short circuit and over load. But the main difference is MCCB have NO & NC contact built in which used for the control circuit. untill and unless MCCB made on control circuit cannot made on(for motor starter feeder) In camparision to MCB, MCCB have higher current rating. And if current rating increases ACB(air circuit breakers used).
So in conclusion All MCB,MCCB & MPCB gives the same protection even can be used in any others place. But MPCB is best for MOTOR protection as it have Inbuilt OVER LOAD RELAY and current range can be selected. Others(MCB&MCCB) may give trouble of unnecessary tripping during starting of motors.For short circuit protection all devices like MCB,MCCB&MPCB functions similar way.
Saroj kanta Nayak
SIEMENS LTD.
KALWA,MUMBAI
Masters In technology from
Nation Institute of technology, Silchar.
| Is This Answer Correct ? | 30 Yes | 2 No |
Answer / chetan
MPCB-MOTOR PROTECTION CIRCUIT BREAKER
MCB-MINIATURE CIRCUIT BREAKER
MPCB TOTALY DIFFERENT FROM MCB AS IT IS NOT ONLY SIMPLE
CIRCUIT BREAKER AS MCB IT HAS INBUILT OVERLOAD RELAY RANGE
IF THE LOAD ON THE MOTOR EXCEEDS ITS CURRENT ABOVE THE
LIMIT OF MPCB IT TRIPS.
MCCB-MOULDED CAGE CIRCUIT BREAKER
MCCB IS A CIRCUIT BREAKER HAVING HAIGH LOAD CAPACITY THAT
IS ABOVE 63 AMPERE WE ARE GENERALY USE MCCB INSTED OF MCB
| Is This Answer Correct ? | 15 Yes | 7 No |
Answer / rohan
MCB(Miniature Circuit Breaker) which ranges from 0.5A to
63A, but now HRC MCB has rating upto 125A, anything higher
than this rating requires a design which can handle so high
current so MCCB(Moulded Case Ciruit Breaker) which has raing
upto 1000A, whereas, MPCB is used for Motor Protection Device.
| Is This Answer Correct ? | 9 Yes | 6 No |
Answer / amu
Dear George M S Kingsley
plz tell me what is the diff b/w lugs and thimbles in electrical field.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rajesh
MPCB means motor protection circuit breaker.its called
manual motor starter.its not a motor its also protective
eqiupment.its working range is 0.1A-25A.MCB(miniature
circuit breaker)and MCCB(molded case circuit breaker)
working range is from the above 10A.
| Is This Answer Correct ? | 9 Yes | 18 No |
Why generator field rheostat is set to maximum position and motor field rheostat is set to minimum?
5 Answers Bhel, College School Exams Tests, TCS, Texas,
Which is stiffer between salient pole rotor and cylindrical rotor synchronous machines? Justify your answer.
How to distinguish between the armature wires with the field wires of a Dc motor ?
physical identification of HT & LT panel
what is the diffrence between kav and kvar?
Hello sir This is prakash from bangalore i have a doubt why we have to maintain DG power factor in the range 0.78 to 0.8 Perhaps i f it is increased means what will happen in DG
what is meant by lagging & leading current
What is the two pole structure?
testing ZNYn11(d) vector group transformer
why phase to phase voltage is 400v while phase to neutral is 220v?
What is resistance of 50meters, 16sq.mm, single core copper cable?
single phase 230v three phase voltage 415volt why we aren't used line voltage 690v?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)