i have D.p. transmitter of range 0 to 2540 mmWC, i want to
use this for flow measurement (0 to 500 ltr/hr.) what
should i do?
Answers were Sorted based on User's Feedback
Answer / g.ramakrishnan
to install flow transmitter and correct range
orifice,ensure that ft output is linear means dcs side u
have to make sq root.if smart type transmitter means
configured sq root output field itself.then u will get
correct reading.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / bari
Install appropriate dp flow element in the flow line with
Beta ratio corresponding to dp of 2540 mmWC for flow of 500
ltr/hr.
Is This Answer Correct ? | 14 Yes | 5 No |
Answer / raees mansoori
use this formula to dcs side Q=K*A*sqrt(H/P) or configured
sqrt output to transmitter side.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / k.sreenivasan
Mr.PasavaRaj,
Your question misses a major point.
Do you have a flow sensor (like orifice or annubar etc)
already installed?If yes, Then you have to match the DP
required by the sensor to the transmitter DP Range.Please
note that 2540 mm wc of the transmitter range can be
changed using communicator (If it is HART) based on
transmitter specifcations.Check what is the minimum span
the tranmitter can be calibrated? if that is greater than
the sensor DP, you have to look for another transmitter.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / pasuvaraj
mr Raees,
Can u explain wat u mean for H & P in this formula, and
also can u explain how the pressure units convert in to
flow rate in the transmitter. I Mean that mm of water colum
is converted into Mass or volumetric flow can u give me the
answer
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jigarsinh vaghela
First of all Good Question
Ans: Use Orifice Bore Calculation sheet
you want process data like pipe size, Max Temp, Max Pressure,
Max Flow rate & Application like Steam or water
put this values in OPA Calculation sheet & you would got dp
range in MMWC
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nadeem iqbal
Dear Sir,if i have flow transmitter range 0 to 2500 mmwc and my DCS range is 0 to t m3/hr ,i m getting 9 Ma how much will be the delta P
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sanjay
by creating proper DP across orifice plates we can measure
flow rate also change the SQRT property in x-mitter
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / guruprasad s.v
i am guruprasad honewell employer.
defenetly we can change configure, this fecility is there
in our company.
Is This Answer Correct ? | 5 Yes | 8 No |
What is the purpose of LO overhead tank in turbines.
what is "smart" in smart transmitter ?
what is virtual instrumentation
all types instrumentation questions want
0 Answers Bhel, Descon, HBL Power Systems,
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
How we will check whether the proximity, which we have is either NPN or PNP, if no data sheet or manual or any details is available to us ???
is here anybody who knows how to calibrate the pressure transmitter? ONLINE
Calibration of flow transmitter.
Valve positioner and actuators in detail.
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
whatis diference between zero pressure and obsolute pressure