i have D.p. transmitter of range 0 to 2540 mmWC, i want to
use this for flow measurement (0 to 500 ltr/hr.) what
should i do?
Answers were Sorted based on User's Feedback
Answer / g.ramakrishnan
to install flow transmitter and correct range
orifice,ensure that ft output is linear means dcs side u
have to make sq root.if smart type transmitter means
configured sq root output field itself.then u will get
correct reading.
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / bari
Install appropriate dp flow element in the flow line with
Beta ratio corresponding to dp of 2540 mmWC for flow of 500
ltr/hr.
Is This Answer Correct ? | 14 Yes | 5 No |
Answer / raees mansoori
use this formula to dcs side Q=K*A*sqrt(H/P) or configured
sqrt output to transmitter side.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / k.sreenivasan
Mr.PasavaRaj,
Your question misses a major point.
Do you have a flow sensor (like orifice or annubar etc)
already installed?If yes, Then you have to match the DP
required by the sensor to the transmitter DP Range.Please
note that 2540 mm wc of the transmitter range can be
changed using communicator (If it is HART) based on
transmitter specifcations.Check what is the minimum span
the tranmitter can be calibrated? if that is greater than
the sensor DP, you have to look for another transmitter.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / pasuvaraj
mr Raees,
Can u explain wat u mean for H & P in this formula, and
also can u explain how the pressure units convert in to
flow rate in the transmitter. I Mean that mm of water colum
is converted into Mass or volumetric flow can u give me the
answer
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jigarsinh vaghela
First of all Good Question
Ans: Use Orifice Bore Calculation sheet
you want process data like pipe size, Max Temp, Max Pressure,
Max Flow rate & Application like Steam or water
put this values in OPA Calculation sheet & you would got dp
range in MMWC
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nadeem iqbal
Dear Sir,if i have flow transmitter range 0 to 2500 mmwc and my DCS range is 0 to t m3/hr ,i m getting 9 Ma how much will be the delta P
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sanjay
by creating proper DP across orifice plates we can measure
flow rate also change the SQRT property in x-mitter
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / guruprasad s.v
i am guruprasad honewell employer.
defenetly we can change configure, this fecility is there
in our company.
Is This Answer Correct ? | 5 Yes | 8 No |
Wht is Dry Leg Calibration and Wet Leg Calibration?
What is protocol ?
how do i tune dearator pr control valve using PID. we set the set point is 0.6kg/cm2 now i want 0.5 to 0.7kg/cm2 limits so what should i give p,i,d values. then pls explain how do set pid values for control valve tuning?
0 Answers SEWA, Sharjah Electricity and Water Authority SEWA,
What is upsampling and downsampling?
what is difference between accelerometer vibration sensor and proximity vibration sensor
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
what is the diffrene between DCS System and PLC System
why we connect digital multimeter in series for dc current measurement and parallel for dc voltage measurement.
How much voltage we get between two wire of 4 to 20 ma output? Is this voltage up or down respectvice to 4 - 20 ma ?
what is mean by process control?
i want to measure temp of hot sand(welding flux) in closed chamber(around 150 deg C).Which is better thermocouple or thermometer?
What is the formula to know the error of weighfeeder after having drop test.