i have D.p. transmitter of range 0 to 2540 mmWC, i want to
use this for flow measurement (0 to 500 ltr/hr.) what
should i do?

Answers were Sorted based on User's Feedback



i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / g.ramakrishnan

to install flow transmitter and correct range
orifice,ensure that ft output is linear means dcs side u
have to make sq root.if smart type transmitter means
configured sq root output field itself.then u will get
correct reading.

Is This Answer Correct ?    17 Yes 3 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / bari

Install appropriate dp flow element in the flow line with
Beta ratio corresponding to dp of 2540 mmWC for flow of 500
ltr/hr.

Is This Answer Correct ?    14 Yes 5 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / raees mansoori

use this formula to dcs side Q=K*A*sqrt(H/P) or configured
sqrt output to transmitter side.

Is This Answer Correct ?    9 Yes 1 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / k.sreenivasan

Mr.PasavaRaj,
Your question misses a major point.
Do you have a flow sensor (like orifice or annubar etc)
already installed?If yes, Then you have to match the DP
required by the sensor to the transmitter DP Range.Please
note that 2540 mm wc of the transmitter range can be
changed using communicator (If it is HART) based on
transmitter specifcations.Check what is the minimum span
the tranmitter can be calibrated? if that is greater than
the sensor DP, you have to look for another transmitter.

Is This Answer Correct ?    5 Yes 0 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / pasuvaraj

mr Raees,

Can u explain wat u mean for H & P in this formula, and
also can u explain how the pressure units convert in to
flow rate in the transmitter. I Mean that mm of water colum
is converted into Mass or volumetric flow can u give me the
answer

Is This Answer Correct ?    3 Yes 1 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / jigarsinh vaghela

First of all Good Question

Ans: Use Orifice Bore Calculation sheet
you want process data like pipe size, Max Temp, Max Pressure,
Max Flow rate & Application like Steam or water
put this values in OPA Calculation sheet & you would got dp
range in MMWC

Is This Answer Correct ?    0 Yes 0 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / nadeem iqbal

Dear Sir,if i have flow transmitter range 0 to 2500 mmwc and my DCS range is 0 to t m3/hr ,i m getting 9 Ma how much will be the delta P

Is This Answer Correct ?    0 Yes 0 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / sanjay

by creating proper DP across orifice plates we can measure
flow rate also change the SQRT property in x-mitter

Is This Answer Correct ?    2 Yes 3 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / guruprasad s.v

i am guruprasad honewell employer.

defenetly we can change configure, this fecility is there
in our company.

Is This Answer Correct ?    5 Yes 8 No

Post New Answer

More Instrumentation Interview Questions

Wht is Dry Leg Calibration and Wet Leg Calibration?

2 Answers  


What is protocol ?

3 Answers  


how do i tune dearator pr control valve using PID. we set the set point is 0.6kg/cm2 now i want 0.5 to 0.7kg/cm2 limits so what should i give p,i,d values. then pls explain how do set pid values for control valve tuning?

0 Answers   SEWA, Sharjah Electricity and Water Authority SEWA,


What is upsampling and downsampling?

1 Answers  


what is difference between accelerometer vibration sensor and proximity vibration sensor

3 Answers  






how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter

1 Answers   HHJ,


what is the diffrene between DCS System and PLC System

5 Answers  


why we connect digital multimeter in series for dc current measurement and parallel for dc voltage measurement.

4 Answers  


How much voltage we get between two wire of 4 to 20 ma output? Is this voltage up or down respectvice to 4 - 20 ma ?

9 Answers  


what is mean by process control?

4 Answers  


i want to measure temp of hot sand(welding flux) in closed chamber(around 150 deg C).Which is better thermocouple or thermometer?

1 Answers  


What is the formula to know the error of weighfeeder after having drop test.

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)