what is the formula for 3 phase motor starting cureent
deatials
3phase 148A delta 415v, efficiancy 94%
can we run the motor with 200A incoming supply
Answers were Sorted based on User's Feedback
Answer / birinchi narayan boruah
It depends upon designed parameter of the motor. Generally
All 3 phase Induction motors take starting current 3 to 5
times of the full load current. 200 Amps incomer can be used
for the same but its better if you go for higher rating.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant
P = 1.732VICosA
I = 148A
Starting current of a motor is 1.25 - 1.5% of I so you
should be able to run the motor but it will be preferable
if yu can go for the next higher rating
Is This Answer Correct ? | 5 Yes | 9 No |
why is the size of earth conductor is half of phase conductor.
1 Answers Century Pulp and Paper, L&T,
What is the tipical Online UPS input voltage for 20 KVA load ( 3 Phase or 1 Phase )? Why ? Explain it...?
Why mostly the HV side of transformer has Delta?
How to find synchronous motor speed formula Ns=120f/P ?....
what is the value of current as well as voltage upto which we will not feel shock and why?
How calculate the MTA in relay?
What is the function of a turbo charger in a 1000kva DG set
why do transformer make a sound
what are the types of starter ?
25 Answers Andhra Sugars, Bhel, Eveready, HyFun Foods, Jindal, ME, Valeo Lighting Systems India Private Limited,
mention hazard experienced during installation
Electricty is generated at around 16kV, then step up to 220kV for transmission then steped down to power transformers then DTs and then through the LT n/w it reaches the consumer end. At the consumer end 230V supply is required. So, why is electricity not generated directly at 230V and transmitted?
What is the range of efficiency of thermal or steam power plants? Why it is so low?