what is the formula for 3 phase motor starting cureent
deatials
3phase 148A delta 415v, efficiancy 94%
can we run the motor with 200A incoming supply
Answers were Sorted based on User's Feedback
Answer / birinchi narayan boruah
It depends upon designed parameter of the motor. Generally
All 3 phase Induction motors take starting current 3 to 5
times of the full load current. 200 Amps incomer can be used
for the same but its better if you go for higher rating.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant
P = 1.732VICosA
I = 148A
Starting current of a motor is 1.25 - 1.5% of I so you
should be able to run the motor but it will be preferable
if yu can go for the next higher rating
Is This Answer Correct ? | 5 Yes | 9 No |