what is use of lockout relay in ht voltage
Answers were Sorted based on User's Feedback
Answer / zan
A lock-out relay is generally placed in line before or
after the e-stop switch so the power can be shut off at one
central location. This relay is powered by the same
electrical source as the control power and is operated by a
key lock switch. The relay itself may have up to 24 contact
points within the unit itself. This allows the control
power for multiple machines to be locked out by the turn of
a single key switch.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / mohammad irfan
Basically it is Master Trip Relay, it takes signal from all the relays and finally trips the breaker.
Is This Answer Correct ? | 1 Yes | 1 No |
1600kva capacity Transformers how the bucholz relay,Oil temperature,winding,surge relay relays setting are to be done
Hi friends. is it possible that SCADA System through RTUs can connect Via PLCC Communication carriers ? thanks
How to select a D.G set for calculated load of 110kW..?
7 Answers Shakthi Power Systems,
why we choose 50 or 60 hertz not other value for the power system?
How can we calculate the motor frame sizes?
What is the Resposiblity of Electrical Utility Engineer
what is the bus bar size of 2700 amp ACB breaker ? and what is the cable size ?pls detailed answer ?
what is a bus riser in power system and why it is used
Auto transformer starter gives the same effect as star/delta strater if its turn ratio = A 0.5 B 0.67 C o.66 D 0.577
What is a commutator?
200-100/1-1A – Transformer Knee point voltage
what is the EMF