What is vcb?
Answers were Sorted based on User's Feedback
Answer / nadarajan v
vcb means vaccum circuit breaker used in ehv power station.
A circuit breaker in which a pair of contacts is
hermetically sealed in a vacuum envelope; the contacts are
separated by using a bellows to move one of them; an arc is
produced by metallic vapor boiled from the electrodes, and
is extinguished when the vapor particles condense on solid
surfaces.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / meenakshi
vacuum circuit breakers. these are the circuit breakers
which are used to protect medium and high voltage circuits
from dangerous electrical situations.
Is This Answer Correct ? | 1 Yes | 1 No |
what will happen if dc supply is given to ac motor?
Yazaki india pvt ltd interview questions qurey related
tell me about vfd
A system absorbs 100 k J of heat and the increase in its internal energy is 100 kJ; the work done is
what is hormonics. how it is generated & what are the problem faced by that.
how MW increase when steam input increase in turbine.
In the ACB breaker capacity is 2000Amp but this each phase taken 1250 But total beldibg load is 600amp or 700amp watt is the problem
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
What is maximum permissible length of cable from transformer (33kV/0.433kV) HT side to HT panel which contain VCB? In which standard i shall get this information.
bitumar
In a single phase converter, the no. of SCR conducting during overlap? a.1 b.2 c. 3 d. 4
Why Water motor is not taking a load or pressure while everything is correct. (Note: Motor running properly)