Answer / raghavendran r
The reverse power relay is used to monitor the direction of
power from A.C generators, if the current in the system
being monitored is reversed, to a value greater than the
customer adjustable preset limit the relay will energise.
The adjustable trip point is 2% to 20% of input current. An
adjustable time delay of 0 to 20 seconds is provided.
Correct setting of the trip point and time delay, will
ensure protection against motoring action of the Syn gen.
An inadverdent relay is used to trip the circuit when a syn
gen has been energised or excited inadvertently.
| Is This Answer Correct ? | 1 Yes | 0 No |
is ac supply can store
Where burned of electricity,when,who, & why.
Difference between ups and invertor
what is HI POT test
Is it possible to protect 3phase overload and earth fault of the 3phase system using two CT's.
What is ignitor and why it is use in Hpmv lamp ?
how to calculate the current carrying capacity of a 25 & 16 kva distribution transformer.
what is the use of breather in transformer?
what is the difference between direct loading and indirect loading?
2 hp motar how many amps taken please show me the formula
I would like to install the largest KW alternator to a 200 amp aluminum bus box in my home. Is it possible to install a 250 KW 400v 251amp synchronous alternator to my home?
how you can select circuit breaker for 2000kva transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)