What is the different type of class in CTS and why it is
required
Answers were Sorted based on User's Feedback
Answer / ganesh
CT's are used in Electrical circuits for different
purposes. For example measurement, protection. In
protection also if it is busbar or differntial protection
the sensitivity of the CT is very important. According to
the purpose it is going to serve the accuracy class of the
CT differs. For measurement it is enough to have low
accuracy class say 10P10 . If it is for Differential or
busbar protection it will be class x which is very accurate
it measurement
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / vimal dixit
Measuring C.T.s - 0.2% class
Protection C.T.s - 5p10 class
AS in measuring cts accuracy of measurement is required.
While in protection cts only mesurement is required.
Is This Answer Correct ? | 1 Yes | 2 No |
What are the factors to be considered during the Synchronization?
If a 1.5V,3W torch light bulb is connected in series with a 15HP/11.19KW,230V single phase motor and the combination is connected against a 230V supply and switched on than what will happen keeping all other parameters as it should be A)the bulb will glow normally B)the bulb will not glow C)the bulb will glow with extra brightness D)the bulb will burn out and if a fuse is connected to the above circuit will something happen to the fuse and what about the single phase motor will it be affected? Please explain with derivation
If the earth is a good conductor of electricity, why don't people get shocked every time they walking on earth?
What is meant by time harmonics and space harmonics?
battery dis charge condition long time condtion?
What are the main parts of VCB?
1.what is difference between ATS & STS main use. 2.what is difference between ACB& VCB With symobles,and main partes, manimum range. 3.How many types of relays and main function.
why the vector group of excitation transformer is YD5(150 deg)how is this factor decided.
what is the disadvantage if earth is connected to neutral
how can we connect the capacitor bank to improve the power factor?
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
What is In (current rating) shown on the MCCB? Is this full load which can withstand by the circuit breaker