What is the different type of class in CTS and why it is
required
Answer Posted / ganesh
CT's are used in Electrical circuits for different
purposes. For example measurement, protection. In
protection also if it is busbar or differntial protection
the sensitivity of the CT is very important. According to
the purpose it is going to serve the accuracy class of the
CT differs. For measurement it is enough to have low
accuracy class say 10P10 . If it is for Differential or
busbar protection it will be class x which is very accurate
it measurement
| Is This Answer Correct ? | 6 Yes | 2 No |
Post New Answer View All Answers
how to calculate short circuit current for the busbar
what is value of Jin transformer
from where the self excitrd induction generator get the power?why is the voltage regulation is poor of seig?
Why we use ups battery and dsdb battery in thermal power plant
(1)The demand for electricity , the amount of renewable generation available, the amount of fossil fuel generation available and the cost of the fossil fuel generation are shown in table below period(hrs) demand(MW) renewable (MW) fossil- fuel(MW) cost of fossil fuel(MW) 00.00 - 01.00 2000 1800 2000 30 01.00 - 02.00 2300 2500 2000 30 02.00 - 03.00 2500 2700 2100 45 03.00 - 04.00 2900 3100 2100 50 04.00 - 05.00 2700 2600 2500 45 05.00 - 06.00 2400 2000 2700 50 06.00 - 07.00 2200 1800 2000 36 07.00 - 08.00 2100 1600 2000 36 Assuming that the renewable generation incurs zero cost, determine an optimal generation schedule(specifying the amount of renewable generation and fossil fuel generation used in each period, the cost for each period and the overall cost for 8 hours.)
what is model question rrb junior engineer electrical gr.II
In ACS 1000 drive we are using 12 pulse converter,why don't use 3 pulse converter.
how can i find ct ratio of meter by seeing name plate of meter and how it should be used in MF calculation if it shows only-/1???
Why using synchronising methed in DG's sets?
how many types control panel of a 132/33 kv substation
What should be the protection scheme for a 15kw, 3-phase motor working in a lathe machine.
hi frds, i m electrical engineer.can i get cdr for electrical engineer if u have then send me on my mail id its jayesh_ee88@yahoo.com.please help me frds
how does high earth to neutral voltage affect electronic equipment?
what will be the effect if you were using different brands of outlets?
What is the difference between Generator Differential Relay and Transformer Differential Relay?