What will be the total current for 300kva UPS if it runs on
40 to 45 percent load. Is there any formula for to
calculate the exact load.
Answers were Sorted based on User's Feedback
Answer / pratheesh
We can calculate the total output current of a 300kva ups.
P=√3*V*I*CosΦ
Where P= Output power of UPS here 300000VA
V= Output voltage of UPS ( I hope this is a 3 phase
415 volts UPS)
I= Output current. (We need to calculate)
CosΦ= Powerfactor of the load. Varies depends the
nature of load(Inductive, Resistive or
Capacitive. We can assume this value is as 1
because we dont know the powerfactor, nature of
load.
So I= P/(√3*V*CosΦ)
= 300000/(1.73*415*1)=Approximately 420A per phase(if
the load distribution is balanced on each phase)
So, If the UPS runs on 40 to 45 percent load, it will take
around 170 to 190 Amps on each phase.
| Is This Answer Correct ? | 14 Yes | 8 No |
Answer / thowsif_emerson_csm team
For 300 KVA the Full load Current=KVA*PF,
i.e 300x.8=240000 Watts.
we know in 3 Phase Circuits,
P=1.732x V x I x Pf,
I=P/1.732xV x Pf,
I=240000/1.732 X 440 X 0.8,
Full Load Current, I =240000/609=394 Amps,
The Load Current @ 40% is 394*.40=158 A(Total Load Current).
The Load Current @ 45% is 394*.45=177 A(Total Load Current).
So load current at 40% Load is 39*.40=15.6 A/Phase Amps.
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / panindra polayadi
p=vI
where p for poore
v for vada
I for idippu
when we apply 40 to 45% load entteammo poore will blast
at that time vada will reduce idippu will be constant it is
newton,s fourth law after somedays newton,s fifth law will
be come beware
| Is This Answer Correct ? | 0 Yes | 4 No |
in GEAFOL Cast-Resin trnaformer of 11/.72kv which has tapping of 11550v,11250,11000,10246v in primary side. To obtain 700v. which tapping should be used of HV side as we have 11000v/720v tapping now .
why a pure inductive circuit has zero power output?
why use only sf6 circuit breker in 400 kv sub station
Is 3 phase induction motor can work as a generator?? if so why & how??
what are tpes of insulaors& its uses
1 Kva = How many HP
what is gridrotor resistance starter
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
hwat type of motor is used in thermal gas turbine hydro nuclear power plants and why
How can we measure and monitor critical performance parameters of Diesel Generator Sets, both electrical and engine ?
what are the problems are there if power factor is leading
why heat produced at junction of two different conductor. what care should be taken to minimize it.
11 Answers Birla, Maihar Cement,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)