What will be the total current for 300kva UPS if it runs on
40 to 45 percent load. Is there any formula for to
calculate the exact load.
Answers were Sorted based on User's Feedback
Answer / pratheesh
We can calculate the total output current of a 300kva ups.
P=√3*V*I*CosΦ
Where P= Output power of UPS here 300000VA
V= Output voltage of UPS ( I hope this is a 3 phase
415 volts UPS)
I= Output current. (We need to calculate)
CosΦ= Powerfactor of the load. Varies depends the
nature of load(Inductive, Resistive or
Capacitive. We can assume this value is as 1
because we dont know the powerfactor, nature of
load.
So I= P/(√3*V*CosΦ)
= 300000/(1.73*415*1)=Approximately 420A per phase(if
the load distribution is balanced on each phase)
So, If the UPS runs on 40 to 45 percent load, it will take
around 170 to 190 Amps on each phase.
Is This Answer Correct ? | 14 Yes | 8 No |
Answer / thowsif_emerson_csm team
For 300 KVA the Full load Current=KVA*PF,
i.e 300x.8=240000 Watts.
we know in 3 Phase Circuits,
P=1.732x V x I x Pf,
I=P/1.732xV x Pf,
I=240000/1.732 X 440 X 0.8,
Full Load Current, I =240000/609=394 Amps,
The Load Current @ 40% is 394*.40=158 A(Total Load Current).
The Load Current @ 45% is 394*.45=177 A(Total Load Current).
So load current at 40% Load is 39*.40=15.6 A/Phase Amps.
Is This Answer Correct ? | 11 Yes | 6 No |
Answer / panindra polayadi
p=vI
where p for poore
v for vada
I for idippu
when we apply 40 to 45% load entteammo poore will blast
at that time vada will reduce idippu will be constant it is
newton,s fourth law after somedays newton,s fifth law will
be come beware
Is This Answer Correct ? | 0 Yes | 4 No |
what is ALF and ISF in current transformer?
What is YNyn Transformer? and what are the other types in this?
how does the rotating m.m.f is produced in the 3-phase induction motor and how the poles are created in 3-phase induction motor ?
How to calculate earth flat size for 250 Kva DG and transformer?
How do ACB are maintenance, what are the problem occurred in ACB
What is the formula to calculate the KVAR value of a capacitor, while value of capcitor in farads is known.
what is the synchronous timer ? and it applications.
can any one help me out by posting something related to rvnl interview for site engineer electrical.? what is the procedure? what kinda question they ask us? how long the interview goes? and any tips? and any thing you want to share?
Why neutral has to switch on-off with phase in TN IT TT systems i.e neutral should be taken as fourth pole
what happens if number of poles in stator and rotor windins of slip ring induction motor are not same. Will it rotate near to the synchronus speed defined by stator?
what is the difference between 3 phase 3wire &3phase 4 wire meter?what is the advantage of 3p3w over 3p4w?
dear friends, how to calculate "Gage" in copper wire , aluminum wire etc. have any formula?