What will be the total current for 300kva UPS if it runs on
40 to 45 percent load. Is there any formula for to
calculate the exact load.
Answers were Sorted based on User's Feedback
Answer / pratheesh
We can calculate the total output current of a 300kva ups.
P=√3*V*I*CosΦ
Where P= Output power of UPS here 300000VA
V= Output voltage of UPS ( I hope this is a 3 phase
415 volts UPS)
I= Output current. (We need to calculate)
CosΦ= Powerfactor of the load. Varies depends the
nature of load(Inductive, Resistive or
Capacitive. We can assume this value is as 1
because we dont know the powerfactor, nature of
load.
So I= P/(√3*V*CosΦ)
= 300000/(1.73*415*1)=Approximately 420A per phase(if
the load distribution is balanced on each phase)
So, If the UPS runs on 40 to 45 percent load, it will take
around 170 to 190 Amps on each phase.
| Is This Answer Correct ? | 14 Yes | 8 No |
Answer / thowsif_emerson_csm team
For 300 KVA the Full load Current=KVA*PF,
i.e 300x.8=240000 Watts.
we know in 3 Phase Circuits,
P=1.732x V x I x Pf,
I=P/1.732xV x Pf,
I=240000/1.732 X 440 X 0.8,
Full Load Current, I =240000/609=394 Amps,
The Load Current @ 40% is 394*.40=158 A(Total Load Current).
The Load Current @ 45% is 394*.45=177 A(Total Load Current).
So load current at 40% Load is 39*.40=15.6 A/Phase Amps.
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / panindra polayadi
p=vI
where p for poore
v for vada
I for idippu
when we apply 40 to 45% load entteammo poore will blast
at that time vada will reduce idippu will be constant it is
newton,s fourth law after somedays newton,s fifth law will
be come beware
| Is This Answer Correct ? | 0 Yes | 4 No |
What is difference between VCB and SF6 breaker
the max. power will be transferred if …… a) sending end vol. is high b) receiving end v is high c)…….. d) corona loss is least
2 Answers Engineers India Limited,
How to set a Zone 1 distance relay for distribution feeder?
0 Answers Schweitzer Engineering,
how to read AWG n how to convert AWG reading into mm?
static chagre
Is a direct shorth ciruit on a branch MCCB in a Low Voltage Switchboard a correct means of tesing the performance for discrimination?
how can calculate 1kva generator running time in 1 liter keroscene
why most of the modern day type electrical appliance have 2 pins rather than 3 pins?
what are different types of alternator and discuss about the methods of cooling
16 Answers Bhel, Jindal, L&T, Nalco, Vedanta,
what is Use of Stones/Gravel in electrical Switch Yard??
how many winding in the single phase transformer?
How out of step protection relay works?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)