What will be the total current for 300kva UPS if it runs on
40 to 45 percent load. Is there any formula for to
calculate the exact load.
Answers were Sorted based on User's Feedback
Answer / pratheesh
We can calculate the total output current of a 300kva ups.
P=√3*V*I*CosΦ
Where P= Output power of UPS here 300000VA
V= Output voltage of UPS ( I hope this is a 3 phase
415 volts UPS)
I= Output current. (We need to calculate)
CosΦ= Powerfactor of the load. Varies depends the
nature of load(Inductive, Resistive or
Capacitive. We can assume this value is as 1
because we dont know the powerfactor, nature of
load.
So I= P/(√3*V*CosΦ)
= 300000/(1.73*415*1)=Approximately 420A per phase(if
the load distribution is balanced on each phase)
So, If the UPS runs on 40 to 45 percent load, it will take
around 170 to 190 Amps on each phase.
| Is This Answer Correct ? | 14 Yes | 8 No |
Answer / thowsif_emerson_csm team
For 300 KVA the Full load Current=KVA*PF,
i.e 300x.8=240000 Watts.
we know in 3 Phase Circuits,
P=1.732x V x I x Pf,
I=P/1.732xV x Pf,
I=240000/1.732 X 440 X 0.8,
Full Load Current, I =240000/609=394 Amps,
The Load Current @ 40% is 394*.40=158 A(Total Load Current).
The Load Current @ 45% is 394*.45=177 A(Total Load Current).
So load current at 40% Load is 39*.40=15.6 A/Phase Amps.
| Is This Answer Correct ? | 11 Yes | 6 No |
Answer / panindra polayadi
p=vI
where p for poore
v for vada
I for idippu
when we apply 40 to 45% load entteammo poore will blast
at that time vada will reduce idippu will be constant it is
newton,s fourth law after somedays newton,s fifth law will
be come beware
| Is This Answer Correct ? | 0 Yes | 4 No |
What is the criteria for deciding whther fire wall is required between two power transformers
How frequency meter measuring frequency? What is the principle of frequency meter?
0.5,1,1.5,2.5,4.0.6.0,10,16 square mm electrical wires how much take maximum current in 50htz
How are calculated the aluminium busbar cross section area?
sir, how to select the cable size, what is the parameters use ang what is the formulas use for this cable size calculations. please tell me.
What is negative sequence over voltage element?
In synchronization circuit what is the function of Interposing voltage transformer(IVT)and Reverse voltage transformer(RVT)
what is the function of impulse relay
In a Capacitor the electric charge is stored in:
2 Answers TELK Transformers And Electricals Kerala Limited,
how to calculate the cable size depending on the transformer rating
why the under of transformer platform is filled with rock stones.
10 Answers TNEB Tamil Nadu Electricity Board,
what is the working principle of electrical motors?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)