What is the criteria for deciding whther fire wall is
required between two power transformers
Answer / dipak thumar
Fire wall is provided to avoid spreading of fire from one
transformer to other.
The height of the wall is to be higher(approx. 1.5 times
that of heighest trafo. ) than the height of the
transformers.
Width of the Fire wall is to be minimum 230 mm if it is
brick wall or 150 mm if it is concrete wall.
This is mendetory in india as per IE rules
Is This Answer Correct ? | 0 Yes | 0 No |
How to calculate energy stored in a capacitance
WHAT HAPPENS IF STARTER OF A FLUROSCENT LAMP IS SHORT CIRCUITED AND WE PUT THE SUPPLY ON?
in a three pin socket y the pin of earthng is longer n bigger...?
Transformers with dc supply
Ht panal kia hota ha?
What is Dry type transformer.How it works
why dc measurements are noted in mc whereas it is mi in ac measurements?
There is any especial requirement for motor to drive through with VFD?
What is the minimum percentage of power that a powerplant can support in ilanding mode ?
Write a note on Treatment for electric shock.
what is the difference between oil surge relay and buchholz relay.
iam interesting to design the control panel for 3 phase pump motors by controling single phase switches.iam plan to use fuse,contactor & relay for motor protection .how can i select the voltage & amps rating for fuse,contactor & relay plz guide me .if anybody clarify my doubt means it will more helpful for my future .