If AVR fails in DG set what will be the affect?
Answers were Sorted based on User's Feedback
Answer / magoola faruku
AVR MEANS AUTOMATIC VOLTAGE REGULATOR-BUT works hand in
hand with the thyristor bridge responsible for
transforming the ac to dc which is used in generating the
ac voltage and at the same time uses the feed back lines
from the output of main ac in line with what is set to
varify wether the ac as per set is ok or not. if not ok avr
requests the bridge to send a more dc or if less then
request to reduce on the dc and as such carrying out the
function of regulation
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vivek g. acholkar
In D.G. set Excitation field is used for generate Voltage.
AVR is used to control Excitation field.If AVR fails the
Voltage will be not generated by D.G.set,but due to residual
magnetism it will running.(If there not available any auto
system to shut down Engine.example--POWERCOM )
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sheikh
DG set AVR Failed means no excitation voltage to generator
then generator ouput e.m.f also will be 00 volts.in this
case generator should goes to shut down in safety of under
voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / malik
AVR is auto voltage regulator that simply means it regulate
the voltage.so if it fails we have to face over voltage
problem.if we want to cheack AVR is faulty or not we have
to bypass AVR by using battry.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / big bull
It depends on whether the DG is connected to grid (infinite
bus) or stand alone. If it is stand alone, there is no
harm, there won't be any terminal voltage. But if the DG is
connected to grid then on loss of field generator draws
reactive power from grid to maintain terminal volatge. As
DG losses the field, it tends to over speed and behaves as
an induction generator.This may cause stability issues with
grid if the grid is small. also
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rahul shukla
if AVR OF DG SET FAIL THEN EMF=0 AND DG WILL BE INDUCTIVE
LOAD IT WILL DRAW REACVE POWER FROM GRID .
Is This Answer Correct ? | 14 Yes | 21 No |
Answer / lokesh
if AVR fails in DG sets emf production will be zero signal
will be sent to Governer engien will shut down
Is This Answer Correct ? | 9 Yes | 25 No |
I know the Capacitor value- 12.5KVAR, voltage 440V gas filled, then what is the formula for calculate the microfarad value for this 12.5KVAR capacitor
1. If we apply dc supply to the primary winding of transformer it will be burnt out. similarly dc supply is given to field winding of syn. motor and armature winding of dc motor, they are safe. (Remember both windings inductive nature) what is the reason behind that?
can we use trip light with bus coupler?
What is the difference between earthing,ground&nutral?
What is the value of specific gravity in charged lead acid batteries.
Why different values of B’s (magnetic flux density) are chosen for DC machines and Induction Motors?
What is the function of stater in tube light circuit?
How to Decide(calculate) Bush bar size for copper and aluminiam ?
State the methods of improving power factor?
Why is the uniform distribution of the capacitor discs in a suspension type insulators essential , what can u do to improve the string efficiency ?
why make protection 85% of winding?
what is relation betn. KW & KV?