If AVR fails in DG set what will be the affect?
Answers were Sorted based on User's Feedback
Answer / magoola faruku
AVR MEANS AUTOMATIC VOLTAGE REGULATOR-BUT works hand in
hand with the thyristor bridge responsible for
transforming the ac to dc which is used in generating the
ac voltage and at the same time uses the feed back lines
from the output of main ac in line with what is set to
varify wether the ac as per set is ok or not. if not ok avr
requests the bridge to send a more dc or if less then
request to reduce on the dc and as such carrying out the
function of regulation
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vivek g. acholkar
In D.G. set Excitation field is used for generate Voltage.
AVR is used to control Excitation field.If AVR fails the
Voltage will be not generated by D.G.set,but due to residual
magnetism it will running.(If there not available any auto
system to shut down Engine.example--POWERCOM )
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sheikh
DG set AVR Failed means no excitation voltage to generator
then generator ouput e.m.f also will be 00 volts.in this
case generator should goes to shut down in safety of under
voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / malik
AVR is auto voltage regulator that simply means it regulate
the voltage.so if it fails we have to face over voltage
problem.if we want to cheack AVR is faulty or not we have
to bypass AVR by using battry.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / big bull
It depends on whether the DG is connected to grid (infinite
bus) or stand alone. If it is stand alone, there is no
harm, there won't be any terminal voltage. But if the DG is
connected to grid then on loss of field generator draws
reactive power from grid to maintain terminal volatge. As
DG losses the field, it tends to over speed and behaves as
an induction generator.This may cause stability issues with
grid if the grid is small. also
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rahul shukla
if AVR OF DG SET FAIL THEN EMF=0 AND DG WILL BE INDUCTIVE
LOAD IT WILL DRAW REACVE POWER FROM GRID .
| Is This Answer Correct ? | 14 Yes | 21 No |
Answer / lokesh
if AVR fails in DG sets emf production will be zero signal
will be sent to Governer engien will shut down
| Is This Answer Correct ? | 9 Yes | 25 No |
what are the applications of PLC?
Why we are use dol starter up to 10 hp
how do we calculate length of starting time and repeated starting of a direct online starter?
How stabilizer works??
why the current leads voltage in the case of a capasitor
Why DC exitation to AC Generator? Why not AC?
what is the difference b/w KVA and KW? the transformer are mentioned KVA rating and the loads are mentioned KW.why?
what is humming noise and wha is the reason to develop humming noise in a mv pannel ?
Why earthing is necessary for any equipment?
oil sample dielectric test gives the insulation rupture voltage at 26 kv. is this transformer safe to be operated . The working voltage is 11 kv
what is the difference between current voltage transformer and current transformer and where it is used?
how to calculate the breaking capacity of different breakers.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)