In Slip ring Induction Motor we use Liquid Rotor Starter
for Starter Every Time Liquid Filling we need add Soda
Sodium Carbonate or only Distilled water is Enough.
Answers were Sorted based on User's Feedback
Answer / amit khamesra
in LRS, the moving contact move towards the fixed contacts,
in water as per rpm feedback. Keeping normal water as
electrolyte will have high resistance value. So to increase
the conductivity of the electrolyte, salt sodium carbonate
is added in water.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / ganesan.p
IN lrs, the moving contacts move towards the fixed contacts
but it is not as per RPM feedback, remaining thing is correct
| Is This Answer Correct ? | 1 Yes | 0 No |
A FIELD MAGNET IS EXITED BY AC/DC?
When calculation of fault current and fault Kva is to be done,why always we use per unit value and why we consider the base kva?
What is bus-bar?
can we use existing 6300V alternator for generating 6600V by increasing excitation,what are advantages & disadvantages to alternator & motors of 6600V.
where transformer is installed? a)generating station b)substation c)voltage regulating area
what is the profesional board for electrical engineer what is thepast and during construction for electrical engineering
What is Reactance & Impedance? what is diffrence between these?
How to calculate the Sizes of the cable required for one specific load? Is there any formula for that? ( EX: For 400KW load,50mtr Length, What is the LT cable Size required?)
In case of power/distribution transformer what is percent impedence?
I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.
resistivity of copper
In more then 1 phase bulb will glow are not?if yes then how it will glow?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)