DEAR ALL
I have motors ( 10 units )each one is 90kw 380V 50 HZ 1000rpm
but new local pwer is 220v 60 hz
requierd rpm should be 1000
pleas what the beast solution is used frequncy converter or
rewinding all motos or chang all motors
thanks
Answers were Sorted based on User's Feedback
Answer / s.sakthivel perambalur
DEAR NOW AUTOMATIC FREQUENCY DRIVE AVAILABLE UPTO YOUR
REQUIREMENT (SIEMENS MAKE)
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / shoeb
yuo need two cdevice one is auto transformer from which yuo
can adjust the voltage and other is cyclo converters whisc
can vary that 60hz frequency to 50 hz
Is This Answer Correct ? | 3 Yes | 0 No |
VFD/ gear box is mandatory as 1000 rpm can not be the
synchronous speed with supply at 60Hz.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anjireddy boduggam
It is mandatory to install two devices:- 1) one device for
voltage adjustment 380v/220v 2)second device for HZ
Converter from 50hz/60hz, but as per technical knowledge
better to change them to suitable motors for 380 Volts / 50
HZ as the cost of Transformers (9nos.) and frequency
converters(50 HZ./60 HZ.) is more than the requirement.
Is This Answer Correct ? | 0 Yes | 0 No |
The existing motors cannot be used. Voltage and frequency
is wrong.
The second issue is the speed - 1000 rpm uses a 6 pole
motor at 50Hz. 6 pole at 60Hz is 1200 rpm and 8 pole is 900
rpm.
You will need to change the voltage and frequency.
If the motors are belt drive changing the ratio of the
pulleys will fix the problem of speed.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k m sarafuzzaman
We Have to instolation A step up transfarmer.
Is This Answer Correct ? | 1 Yes | 5 No |
During the main stator winding insulation testing (phase to ground)of 11kv alternator (Lerysomer) i found 0 and resistance with multimeter and found 20 killo ohm while the power cables are connected both end (Generator & VCB). In VCB PT (Potential transformer) are connected. Please any body explain that method of insulation is correct or not? also describe of PT connections
What is mean by making & breaking capacity of circuit breakers?
how to test vector goup of Dy11 transformer
Why induction motor is widely used in industry
draw tube light circuit
Hi ,what the accurate method to set correct(In) over load to protect the 3~ motor
Hi all I had applied for the RRB test in the ELECRICAL category. I would be pleased if any of you can sent me previous year question papers. Please forward the question papers to varshashahi@yahoo.com Thanks and regards Varsha
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
Difference between 3.5 core and 4 core
What is the formula to calculate the rating of a three phase trnasformer
why all the feeders are designed in a particular manner ... is there any reason for that???
when ELCB breaks the circuit than INVERTER auto-connect the circuit to the battery than how can the operetor is safe??