Answer / gaurang
As per Equation
P=route 3 * V *I* cos phi
I=KVA/ rout 3 * V
So for 2000 KVA Transformer and considering Volatge 415 V.
I=2000/1.732 * 0.415
I=2782 A
Considering the breaker rated capacity selection above 2782
A as per Mfg. std.
Circuit breaker capacity will be of 3200 A.
Is This Answer Correct ? | 27 Yes | 0 No |
Answer / ashish patil
First find the full load current of transformer.2MVA
transformer current value comes near 2915 A. consider
overloading capacity 10%. it comes near 3100.
so u can select indor Air circit braker or 4000A
capacity.
Is This Answer Correct ? | 29 Yes | 13 No |
Answer / solver
gaurang you are right
also mukund is right
Dear ashish & sareer,
always remember that the LT side breaker of transformer
is only selected based on rated capacity of LT winding.
i.e. 2782 A in this case.
& no overloading is considered beyond capacity of
transformer winding.
besides that transformer is loaded to 80% of its capacity.
This makes the load current even lesser than the rated.
Hope you are satisfied by this answer
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / sareer ahmad lone
Ans.First you have to find out the full load current of the
transformer that is IL=2915A then as per NEC you have to
give atleast 25% that is 2915x1.25=3643.75A.So the nearest
size of Circuit Breaker shall be 4000A.
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / mukund
it is necessary to know what is the voltage rating of
transformer
many of the times 2000 kva x'mer are 22/11 kv less than
that are generally 22/0.415kv or 11/0.415kv first you
clear that
Is This Answer Correct ? | 8 Yes | 6 No |
Answer / foolinla
The capacity of a transformer depends on its rated voltage
and current. The load current varies depend on the voltage
of the transformer.
If this 3 phase 2000KVA has a primary voltage @ 4160V, then
the primary current is 278A (2000000/1.73/4160V)
If the secondary of this 2000KVA is 480/277 then the
secondary full load current is 2408A (2000000/1.73/480).
If the secondary of this 2000KVA is 208/120 then the
secondary full load current is 5558A (2000000/1.73/208).
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aravind
WHile selecting any Circuit breaker the transfoemer rating
and Impedance should be considered.
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / khadu ali murthuja
Transformer rating already given=2000KVA
Select Air circuit breaker ie secondary current multiplying with 1.6A to the rating of the transformer.
secondary current = 2000×1.6
= 3200A Air Curcuit Breaker Required.
since 1KVA =1.6A
how to find out primary current.
the relation ship between voltage and current.
V2/V1=I1/I2
415/11000=I1/3200
I1=120A...
Is This Answer Correct ? | 0 Yes | 1 No |
How to determine earth fault level to set relay for a normal distribution system of 11 kV , 100 A load????????
Why are tertiary windings used in transformers?
why we grounding the neutral of a transformer?
What is the difference between a 3 winding and 2 winding Potential Transformer
For high frequency application we use which transformer?
IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?
what is AVR in alternator how its work?
HOW can i REuse the fused MLL LAMPS & GLS LAMPS at our factory
what is the permissible bend in the LT& HT CABLES.
Whats the type of current and potential transformers?
There is air in a room . the top and bottom of the room are at constant temp. T1 and T2. DRAW THE temp profiles if a. T1 greater than T2 b. T1 less than T2
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,