WHAT IS THE THUMBRULE FOR FINDING OUT THE CURRENT CAPICITY
OF A COPPER WIRE?? 2.5, 4, 6MM SQUARE ETC...
Answers were Sorted based on User's Feedback
Answer / uttam dutta
cURRENT CARRYING CAPACITY NOT ONLY DEPENDS ON THE CROSS
SECTION OF THE COPPER WIRE, IT ALSO GREATLY DEPENDS UPON
THE TYPE AND THICKNESS OF THE INSULATION, ONE MORE FACTOR
IS CORE OF THE CABLE, IE SINGLE CORE OR MULTICORE.
cONSIDERING ALL THIS FATORS STRICTLY IT CAN BE SAID 1 SQ.
MM COPPER CABLE CAN BEAR MAX.11 AMP SAFELY CONTENIOULY AND
2.R CAN BEAR 19 AMP . 4 SQ MM CAN BEAR 26 AMP. SOME TIME
THIS MAY VARY LITTLE DEPENDING UPON MAKE.
| Is This Answer Correct ? | 7 Yes | 4 No |
Answer / sonam
CURRENT DENSITY OF CU IS 1 AND AL IS 0.7.FROM HEREU CAN
FIND CURRENT CARRYINGCAPACITY IF U HAVE AREA
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amro
depend the weathier out side the cabel
1- temperature
2- length of the cable
3-load factor
4- the cabel throw ( in air &duct & pipe &cabel tranch&
cabel leader inside the tranch)
for exampel:-
i= power/ volt* cos@
after that let used cabel 4 mm2
look in the catlog cabel and taking the rated current
oppset the wire
rated current *load factor*factor group*factor throw (in
air &duct & pipe &cabel tranch& cabel leader inside the
tranch )*factor temprature =current
1- if more then the load current ites ok
2- if less then the load current ites no must be chose the
big size cabel and again
calculate the equation and so an
after the calculate the voltge droop presentage must be
less the _+ 5 % from the main voltge
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / raju
in case copper wire we usually take 4(approximately) amps
per square mm
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / ramesh kumar k
No.. No.. Mr. Raju... it is 2A/sq.mm atmost for safe
operation... other wise copper wire will burn out...
so the thumb rule is the current carrying capacity is
double that of area...
| Is This Answer Correct ? | 2 Yes | 8 No |
why do mostly prefer to generate and distribute electricity in 3 phase..not in 4 phase or 5 phase.??
what is power frequency withstand and impulse withstand of a circuit breaker?
what is the current limit of lighting arrester ?
What is the differences in phase to phase voltages between star and delta connections of stator?
What is the use for cable entry in control room?
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
what is motor?
Can we get the shock if Power system is unearth means delta type take an rated voltage as 6.6 KV?
i need online ups battery calculater
how much earthings are mendatory at a 25kva sub station?
In the UVR(Under Voltage Relay) there is a knob for the hysteresis setting. what is this setting? its threshold is given from 5% to 50%. please help me....
in three pin pluge there three pins one is phase and second is earth third is nutral why nutral high diameter compare with phase and earth
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)