Answer / mahesh sali
For Cal.the cable size , pl. see the below size
1) Cal. the full loasd current of motor
2) cal. the voltage drop from ht starter panel to motor at
starting and running .
3) as per IEC rule u should take the 20% additional to ur
selected size of cable.
Base on the above step we can easily cal. the size of cable
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / manoj
Calculate steady state voltage drop and motor starting voltagedro they should be within limit also the short circuit withstand capacity to satisfy i2t
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the formula to find out two phase active & reactive power
name the famous power plants in ap and vwhere it is located with capacity details
I had applied for JE in PSEB, Can you pls send me the Question bank for related to my field
Any formula to calculate neutral current in 3 phase 4 wire system
how am i achived model paper to prepratio for bhel exam
How do you find HT and LT sides of a distribution transformer only by looking at it from outside?
why generator is star connected ?
what reactive how to maintain
Define what is difference between fuse and breaker?
Explain the operation of damper winding
WHY PROTECTION CT IS USED NEXT TO METERING CT?
What are the two segments of nyquist contour.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)