why earthing is not required on transformer prymary winding
side ???
Answers were Sorted based on User's Feedback
the neutral is generated at the secondary side of the t/f,
so the earthing is done at sec. called the dedicated
earthing. but at the pr. side of the t/f no neutral is
generated hence require no earthing. but the body of t/f
is also earthed.
Is This Answer Correct ? | 18 Yes | 2 No |
Answer / jackson
If the primary side of the trasformer is delta, then only
body earth required.delta no eathing is required because
upstream is delta circuit which increase the reliability of
power transmission if earth fault occur. in delta circuit,
no earth fault will be detected.
Is This Answer Correct ? | 14 Yes | 2 No |
Answer / t eswara rao
In any type of circuit, the neutral is earthed at source side
In transformer case, the secondary voltage acts as the
source voltage to the load and hence the secondary neutral
conductor is must be earthed.
The secondary currents are transformed in to primary
currents by induction principle. and hence primary side
neutral is not required to be earthed. In other words, the
primary winding acts as load circuit for the partial network.
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / shahzad
In case of DELTA/Star Power transformer, the secondry is
solidly earthed because the zero sequance current ciculate
in delta and in star side if ther is no neutral earthed the
protective relay will give false tripping so it is neutral
of secondry is earthed
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / lokeshraj
A power t/f is delta/ star type. Delta side can not be
earthed even there is no need to make in earth as f the
secondary is earthed there will be no or very less fault
current. So the primary will also be safe as no change in
secondary current means no change in primary..
Please post you feedback..
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / dj
Transformer Primary side is Delta Connected, so there we
dont provide Earth fault Protection thats why it is not
solidly earthed, only earthing is provide at transformer
body. But on the secondry side which is usually star
connected, we have to provide solidly earthing to neutral
so that we can use earth fault protection system.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / mahi
HI EVERYBODY, I HAVE A SMALL DOUBT ON THE POWER TRANSFORMER
EARTHING. ACTUALLY THE TRANSFORMER IS DELTA/STAR TYPE, THE
SECONDARY SOLIDLY EARTHED, I HEARD THAT THE PRIMARY SIDE OF
THE TRANSFORMER RESISTIVELY EARTHED. CAN SOMEONE MAKE ME
CLEAR, WHAT RESISTIVELY EARTHING AND HOW IT HAS TO BE
DONE.....???
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / theo
The primary side you don't earth otherwise if you measure on the secondary side there will be no voltage be induce on the secondary side because it will go straight to earth if you provide an earth. there a induction happening between primary and secondary side.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bk
We use earthing for Body Protection.
So there is no meance of Prymary or Secondary.
Between phase we use neutral but for Secondary side
Prymary side Delta connection so we don't use neutral.
Is This Answer Correct ? | 4 Yes | 4 No |
2. What are the parameters of EHT sub-station?
1 Answers APGenco, Blue Star, Enercon,
what is lxr?
how dia of wire and angles are calculated for overhead shielding wire to protect substation equipment from lightening strokes???
Hi guys! Plz help me to answer the following questions. 1. What are the types of transmission line energy losses? 2. Why are the VLF are used some types of services? 3. What frequencies are used for reliable beyond the horizon terrestrial communication without repeaters? 4. To permit selection of 1 out 16 equi-probable, what is the number of bitis required? 5. What is the most common modulation used for telegraphy? 6. What is the multiplexing is used to increase the capacity of the optic fiber? Thanks
if i get a drop in my 1st year and the i clear my 2nd year and 3rd year all clear and i dont have any back logs so can i be able to sit in campus selection??
If my sfu is 64 Amp & its link is 32 Amp then at what amp.my sfu will trip???
what is the diffference between 3 point and 4 point starter ?
If two generator running parallel, at that condition both ngr Taken in line or taken any one ngr, but why any one or both Ngr in line? Ngr is use for which purpose?
According to IEC60034-14, When the vibration monitoring system required for motor Bearing. above which KW, it is required? and for what type of bearing the vibration probe is provided.
if u have to run a 300kw moter then what is ur choice HT or LT switchgear & explain why?
What is the difference between a verilog task and verilog function?
how do prepare ongc exam.how is it question model.i am electrical. which part covering in electrical.tell me