Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why earthing is not required on transformer prymary winding
side ???

Answers were Sorted based on User's Feedback



why earthing is not required on transformer prymary winding side ???..

Answer / ankush miglani

the neutral is generated at the secondary side of the t/f,
so the earthing is done at sec. called the dedicated
earthing. but at the pr. side of the t/f no neutral is
generated hence require no earthing. but the body of t/f
is also earthed.

Is This Answer Correct ?    18 Yes 2 No

why earthing is not required on transformer prymary winding side ???..

Answer / jackson

If the primary side of the trasformer is delta, then only
body earth required.delta no eathing is required because
upstream is delta circuit which increase the reliability of
power transmission if earth fault occur. in delta circuit,
no earth fault will be detected.

Is This Answer Correct ?    14 Yes 2 No

why earthing is not required on transformer prymary winding side ???..

Answer / t eswara rao

In any type of circuit, the neutral is earthed at source side
In transformer case, the secondary voltage acts as the
source voltage to the load and hence the secondary neutral
conductor is must be earthed.
The secondary currents are transformed in to primary
currents by induction principle. and hence primary side
neutral is not required to be earthed. In other words, the
primary winding acts as load circuit for the partial network.

Is This Answer Correct ?    7 Yes 3 No

why earthing is not required on transformer prymary winding side ???..

Answer / shahzad

In case of DELTA/Star Power transformer, the secondry is
solidly earthed because the zero sequance current ciculate
in delta and in star side if ther is no neutral earthed the
protective relay will give false tripping so it is neutral
of secondry is earthed

Is This Answer Correct ?    3 Yes 0 No

why earthing is not required on transformer prymary winding side ???..

Answer / lokeshraj

A power t/f is delta/ star type. Delta side can not be
earthed even there is no need to make in earth as f the
secondary is earthed there will be no or very less fault
current. So the primary will also be safe as no change in
secondary current means no change in primary..

Please post you feedback..

Is This Answer Correct ?    2 Yes 0 No

why earthing is not required on transformer prymary winding side ???..

Answer / dj

Transformer Primary side is Delta Connected, so there we
dont provide Earth fault Protection thats why it is not
solidly earthed, only earthing is provide at transformer
body. But on the secondry side which is usually star
connected, we have to provide solidly earthing to neutral
so that we can use earth fault protection system.

Is This Answer Correct ?    3 Yes 2 No

why earthing is not required on transformer prymary winding side ???..

Answer / mahi

HI EVERYBODY, I HAVE A SMALL DOUBT ON THE POWER TRANSFORMER
EARTHING. ACTUALLY THE TRANSFORMER IS DELTA/STAR TYPE, THE
SECONDARY SOLIDLY EARTHED, I HEARD THAT THE PRIMARY SIDE OF
THE TRANSFORMER RESISTIVELY EARTHED. CAN SOMEONE MAKE ME
CLEAR, WHAT RESISTIVELY EARTHING AND HOW IT HAS TO BE
DONE.....???

Is This Answer Correct ?    1 Yes 0 No

why earthing is not required on transformer prymary winding side ???..

Answer / theo

The primary side you don't earth otherwise if you measure on the secondary side there will be no voltage be induce on the secondary side because it will go straight to earth if you provide an earth. there a induction happening between primary and secondary side.

Is This Answer Correct ?    1 Yes 0 No

why earthing is not required on transformer prymary winding side ???..

Answer / bk

We use earthing for Body Protection.
So there is no meance of Prymary or Secondary.
Between phase we use neutral but for Secondary side
Prymary side Delta connection so we don't use neutral.

Is This Answer Correct ?    4 Yes 4 No

why earthing is not required on transformer prymary winding side ???..

Answer / ravi

mr prashanth if u dont know the answer u not suppose to
blame any of the answers.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the meaning of "i.p.-43" and duty cycle-s1 on the name plate of a asynchronous machine?

1 Answers  


what is the role of energy meter in distribution system ?

0 Answers  


what is the write prosidure of stringing of 8meter pcc pole.

0 Answers  


Is 3C x 2.5 Sqmm Cable can withstand 40Amp Starting current? If Yes then specify your ans.

2 Answers   NTPC,


How to calculate the Short Circuit Impedance in Transformer?

3 Answers  


the cheapest inducting instrument among all is a)pmmc b)moving iron c)electrodynamometer d)rectifier

2 Answers   APCPDCL, APEPDCL,


What are the different modes of plc processor?

1 Answers  


send me any model test paper of clerical post of state bank of india.......

0 Answers  


How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side?

1 Answers  


what's burden resistor, why it's used?

1 Answers   Bhel, TVS Group,


advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor

0 Answers  


they conducted technica for 1 hour..i also managed..they selected 5 boys and only one girl,myself got wait listed.whether they would call or not

2 Answers   MAHINDRA,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)