I have 2 Nos of 2500kVA 33/0.415V cast resin transformers.
How to decide on ampere rating of HT Panel?
Also advise me how many panel RMG i have to consider
whether 4 panel ok?
you have not mentioned the 33kv source. is it fed from one
source or two sources.
your transformer rating is 2500kva, 33/0.42 48/3500A.
THERE IS NO 100A.33KV SW.GR
THE MINIMUM RATING IS 400A,33KV METALCLAD SW.GR, 25KA/1s.
if the sorce is one ,then 3 panel of 33kv sw.gr enough.
If the source is two,then four panel required.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the ideal position cooling fan inside the dc motor?
how we select ac fuse rating of an power inverter???
how many stairs have you climbed while you were coming
if we give 60 hz single phase supply to the transformer used in europe , than what will happen
If an induction motor is restarted before its rotor stop rotating, then what will be the amount of current drawn? Is this current will be the same as motor starting current?
What is meant by reactance voltage?
some meggers have three terminals. wat is the real function of the earth terminal?
How much duration I can keep open the CT if it is under loading condition(100 Amp load)?
3 Answers Infosys, NTPC, Suzlon,
How to calculate the FUSE rating?
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
how to calculate unit consumption on 3phase 380-415 v0lt kilowatt motor eg ( 55kw,380v,3phase 50-60hz)
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.