why does chattering take place in ac contactors?
can it be avoided & what care does the manufacturer take to
eliminate this phenomenon????
Answers were Sorted based on User's Feedback
Answer / terence
low voltage or voltage drop will cause them to chatter.
Is This Answer Correct ? | 43 Yes | 9 No |
Answer / srij21
Apart from the above correct answer,chattering may happen
aslo due to the loose supply wire given to the contactor
coil and also on the coils magnetic effect.
Is This Answer Correct ? | 28 Yes | 11 No |
Answer / reshi
Chattering will occur when there is no perfect contact
within the contactor, when chattering occurs the two
contacts may get weld together.This may cause a danger when
it is required to open the circuit or required to stop the
motor from the remote option.Chattering may also occur if
the contactor is undersized w.r.t load current.
Is This Answer Correct ? | 24 Yes | 12 No |
Answer / korra
Can be either one of these;
1) Low voltage condition.
2) Improper armature alignment.
3) Broken shading coils.
Is This Answer Correct ? | 3 Yes | 0 No |
chattering occurs due to many conditions:
1. due to loose contact
2. dust contents
3. new product will not get contact very quickly but after some periodic operation it will be rectified.
4. under coil rating e.t.c
so major is no 4 & 2 this shall be taken care by manufacturer
Is This Answer Correct ? | 13 Yes | 11 No |
Answer / kyle
Chattering us usually due to a loose neutral.
Swap out all mechanical contactors with mercury contactors, and be done with it.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / bhanu dudhat
i agree with above answer and
also manufcture can add
sheded pole ring when it
design bcoz ac current flow
positive ok but naturle side
pick up not possible so and
thats reasen they add sedded
pole ring for continios hold
contactor.
Is This Answer Correct ? | 1 Yes | 20 No |
Answer / selvakumar
my opinion to buy schneider electrical contactor is the best one,,,,,,,,,chattering not occur in that contactor,,,,,,,,,,
Is This Answer Correct ? | 0 Yes | 22 No |
a simple c++ program to calculate simple interst with its data members as private
Whot is the difference between MCB and MCCB.Whot is the selection critearea for MCCB and MCB for 63 Amp.
meaning of two lines in between the transformer single line diagram??
why the AC or DC motor takes high starting current?
why the all high voltage transformers are in 11kv , 33kv , 66kv, 132kv like that
How to know the following data of synchronous generator 1. D-Axis Unsaturated Reactance 2. D-Axis Unsaturated Transient Reactance 3. D-Axis Unsaturated Sub - Transient Reactance
which subject is better to tell when hr asks the area of interest?..
tell me any book for current n potential trasformer with full knowledge ?
1.After synchronising the alternator to the grid,how we r delivering power to the grid?if the i/p increases does the speed hence frequency increases? 2.y the power factor is changing when exitation changes?what is the relation with p.f and flux?
you are a electrical student, why are you coming for software job.
what is basic difference betmeen normal & flame proof motor??
what is mean by amf