WhY PF low at Time of PT Missing in HT Meter
Answers were Sorted based on User's Feedback
Answer / abdul salam
Power factor is the quotient of KW to KVA, in this
perticular case when PT is missing in one phase then the
voltage which is seen by the meter will increase as a
result KVA will increase and hence low PF.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / dave.vimal
When One phase PT missing. HT consumer is always used three
phase load . This time consumer is not using load but
capacitor bank is on . so power factor is low and lead
Is This Answer Correct ? | 2 Yes | 4 No |
why transformer cannot rotate though the princplebehind induction motor is similar to a transformer?
What is transformer saturation?
I am having dual speed motor of cromton greaves make of 3.7 KW -1400 rpm and 5 KW - 900 rpm. Please let me know groups and winding connction for rewinding purpose.
Can we use the Poly Phenly Sulphide instead of Poly Phenly Ether? Do clarify your opinion.
Will transformer heating be approximately the same for resistive, inductive or capacitive loads of the same VA rating? Explain.
For 7.5HP motor 2880rpm 415VAC Connected with Pressurisation Fan we used Star Delta Startor why not we use DOL startor
what is the carona effects meaning in HT line transmmission system
why motor rating in kw?
what is the function and use of oil filled cables specify its advantages and disadvantages
is 3-phase induction motor need a starter ? why do it so
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
IN A DY11 GROUP DISTRIBUTION TRANSFORMER WITH NEUTRAL EARTHED, WHAT WILL HAPPEN TO THE SYSTEM VOLTAGE & THE EQUIPMENTS IF EARTH GETS OPEN ON LOAD?