What is RTCC in a transfomer and specify its function.
Answers were Sorted based on User's Feedback
Answer / yash
RTCC is Remote Tap Change Circuit is connected to OLTC of
Transformer through control cables. It raise & lower the
voltage as accordingly specified by controlling the motor
drive in OLTC electrically (and manually through Push
Buttons)
In RTCC an AVR (Automatic Voltage Regulator)is fixed to
maintain the output voltage level(raise & lower) by
controlling the motor.
Is This Answer Correct ? | 369 Yes | 21 No |
Answer / sanketh
RTCC is a panel it should be place in the electrical room
for Remote Tap changing.It must Required while OLTC is used.
Is This Answer Correct ? | 201 Yes | 19 No |
Answer / joy banerjee
In transformers Output Voltage can be controlled either by
Off Circuit Tap Changer (Manual tap changing)or By On -
Load Tap Changer-OLTC (Automatic Changing).
In the transformer with OLTC, it is a closed loop system,
with follwing components:
#1. AVR (Automatic Volatge Regulator- an electronic
programable device). With this AVR we can set the Output
Voltage of the transformers. The Output Voltage of the
transformer is fed into the AVR through the LT Panel. The
AVR Compares the SET voltage & the Output Voltage and gives
the error signal, if any, to the OLTC through the RTCC
Panel for tap changing. This AVR is mounted in the RTCC.
#2. RTCC (Remote Tap Changing Cubicle):This is a panel
consisting of the AVR, Dispaly for Tap Position, Voltage,
LEDs for Raise & Lower of Taps relays, Selector Switches
for Auto Manual Selection... In AUTO MODE the voltage is
contrlled by the AVR. I manual Mode the operator can
Increase / decrease the voltage by changing the Taps
maually through the Push Button in the RTCC.
#3. OLTC is mounted on the transfomer. It consits of a
motor, controlled by the RTCC, which changes the Taps in
the transformers.
Is This Answer Correct ? | 111 Yes | 7 No |
Answer / arun babu.s
RTCC is " Remote Tap Change Centre " which is a
programmable device to control the output of the transfomer
thro'OLTC unit fitted in the transformer through control
cables.
The desired voltage will be achieved accordingly by
controlling the OLTC with respect to the tap position
through RTCC system.
The output voltage of the transformer is been maintained
through an inbuilt AVR (Automatic Voltage Regulator),which
continuously verifies the output power with the set /
programmed reference voltage.Which triggers the OLTC
accordingly.
Hence,by above said phenomena,the consistency of the
transformer output is been maintained.
Is This Answer Correct ? | 70 Yes | 9 No |
Answer / rahul kumar
In transformers Output Voltage can be controlled either by
Off Circuit Tap Changer (Manual tap changing)or By On -
Load Tap Changer-OLTC (Automatic Changing).
In the transformer with OLTC, it is a closed loop system,
with follwing components:
#1. AVR (Automatic Volatge Regulator- an electronic
programable device). With this AVR we can set the Output
Voltage of the transformers. The Output Voltage of the
transformer is fed into the AVR through the LT Panel. The
AVR Compares the SET voltage & the Output Voltage and gives
the error signal, if any, to the OLTC through the RTCC
Panel for tap changing. This AVR is mounted in the RTCC.
#2. RTCC (Remote Tap Changing Cubicle):This is a panel
consisting of the AVR, Dispaly for Tap Position, Voltage,
LEDs for Raise & Lower of Taps relays, Selector Switches
for Auto Manual Selection... In AUTO MODE the voltage is
contrlled by the AVR. I manual Mode the operator can
Increase / decrease the voltage by changing the Taps
maually through the Push Button in the RTCC.
Is This Answer Correct ? | 35 Yes | 3 No |
Answer / praveen
RTCC is Remote tap changer circuit, normaly RTCC panel will
be installed in Main panel room and will be connected to
OLTC ( On line tap changer) of the transformer through
control cable.There will be AVR in RTCC Panel to control
the secondary voltage of the transformer and AVR output
will control OLTC motor in Clock wise or Anty clock wise.
and also there will be selection in RTCC panel for Auto and
manual operation.
Is This Answer Correct ? | 32 Yes | 7 No |
Answer / lalit pratap
RTCC full form is (Remote tap change Control) it's using in OLTC (On Load Tap Changer)installed transformers for voltage regulation controll.
Is This Answer Correct ? | 23 Yes | 1 No |
Answer / rajeev
RTCC refers to Remote tap changer cubicle.
It is used to change the tap of transformer from LT panal
room whith the help of remote circuit.
Is This Answer Correct ? | 27 Yes | 6 No |
Answer / ajay kumar singh
RTCC IS REMOTE TAPCHANGER CONTROL CUBICAL WHICH IS ESTABLISH IN CONTROL ROOM OF SUBSTATON, IT IS REQUIRED WHEN OLTC IS USE IN POWER TRANSFORMER,AVRR(AUTOMATIC VOLTAGE REGULATER RELAY)MOUNTED ON RTCC PANEL WHICH SET UP SECONDARY VOLTAGE OF TRANSFORMER FOR AUTO MODE ONLY
Is This Answer Correct ? | 16 Yes | 5 No |
Answer / anand
RTCC IS REMOTE TAP CHANGE CUBICLE , WHICH GOVERNS THE
VOLTAGE CONTROL OF THE TRANSFORMER THROUGH AVR OR BY MANUALLY.
IT HAS ANNUNCIATOR (MICROPROCESSOR BASED PROGRAMMING)WHICH
ALARMS THE OPERATOR DURING THE FAILURE OF FAN ETC.
Is This Answer Correct ? | 12 Yes | 7 No |
how to calculate full load current of transformer & induction moter ?
what happens when a power transformer neutral earthing broken???
what is formula for zero phase sequence of nuetal earthing transformer of 6.6 kv
What is the relay function?
Why in KVA diesel engine? Why not KW
why abcd parameters are called as transmission parameter?
In the solution of load flow eqation, Newton raphson method is superior to the gauss siedal method because (a)the time taken to perform one iteration in the NR method is less when compared to GS method (b)the number of iterations required in the NR method is more compared to that in the GS method (c)the number of iterations required is dependant on the size of the system in the NR method (d)convergence characteristics of the NR mehod are not affected by the selection of the slack bus
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
Pls explan the OLR setting in VCB at HT yard
How to solve the problem of low voltage at consumer end in distribution system if one phase come low voltage of transformer
We have 250 KVAR cacitor bank & our average load is 200kva but our power factor is average 0.66 how can we maintane it? how can we balance our load?
Why electrical heaters are not provided with overload relays in circuits