What is RTCC in a transfomer and specify its function.
Answer Posted / joy banerjee
In transformers Output Voltage can be controlled either by
Off Circuit Tap Changer (Manual tap changing)or By On -
Load Tap Changer-OLTC (Automatic Changing).
In the transformer with OLTC, it is a closed loop system,
with follwing components:
#1. AVR (Automatic Volatge Regulator- an electronic
programable device). With this AVR we can set the Output
Voltage of the transformers. The Output Voltage of the
transformer is fed into the AVR through the LT Panel. The
AVR Compares the SET voltage & the Output Voltage and gives
the error signal, if any, to the OLTC through the RTCC
Panel for tap changing. This AVR is mounted in the RTCC.
#2. RTCC (Remote Tap Changing Cubicle):This is a panel
consisting of the AVR, Dispaly for Tap Position, Voltage,
LEDs for Raise & Lower of Taps relays, Selector Switches
for Auto Manual Selection... In AUTO MODE the voltage is
contrlled by the AVR. I manual Mode the operator can
Increase / decrease the voltage by changing the Taps
maually through the Push Button in the RTCC.
#3. OLTC is mounted on the transfomer. It consits of a
motor, controlled by the RTCC, which changes the Taps in
the transformers.
| Is This Answer Correct ? | 111 Yes | 7 No |
Post New Answer View All Answers
CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS
How to calculate the sag on transmission Lines.
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
Mention what are the different colors on wires indicates?
What are the internal and external faults?
What is the difference between indoor and outdoor transformer
standard earthing rating for power line..
What is the relationship between voltage,current & frequency?
What is the temperature PROFILE OF A FLUID W. R. T. Distance from a sphere to which it is IN CONTACT which is at constant temp.?
3 phase induction motor connection star or delta while using ac drive motor is .75 to 5.5 kw
What will happen if we on 200kvr capacitor bank(11kv in bus)If there is low load on transformer (1.5 mva 33/11 kv)
When we have earthing mesh or underground earthing network in industrial plants, weather we have NT-S or NT-C-S kind of earthing system, so eventually weather we must use 4 or 5 wire in 400 volt level (For example 3×150+70 mm2 or 5×150 mm2) in this connection I would like to know exactly the paragraph of IEC or IEEE number
while doing high potential for 11KV 3 core cable how much leakage current will obtain?, what will be acceptance value?
How to protect sensitive loads such as Dosing pumps inside a factory from voltage surge/voltage fluctuation.
what is sevice settings for mccb?How can be it setted?