how we are measuring the winding temperature of the
transformer?
Answers were Sorted based on User's Feedback
Answer / vishal shah
hello Mr. V Ram
Windin Temp. Can be measured with the help of Inbuilt-
Thermal Image type WTI (Winding Temp. Indicator)
The Winding is the component with highest temperature
within the transformer and, above all, the one subject to
the fastest temperature increase as the load increases.
Thus to have total control of the temperature parameter
within transformer, the temperature of the winding as well
as top oil, must be measured. An indirect system is used to
measure winding temperature, since it is dangerous to place
a sensor close to winding due to the high voltage. The
indirect measurement is done by means of a Built-in Thermal
Image.
Winding Temperature Indicator is equipped with a specially
designed Heater which is placed around the operating
bellows through which passes a current proportional to the
current passing through the transformer winding subject to
a given load. Winding Temperature is measured by connecting
the CT Secondary of the Transformer through a shunt
resistor inside the Winding Temperature Indicator to the
Heater Coil around the operating Bellows. It is possible to
adjust gradient by means of Shunt Resistor
In this way the value of the winding temperature indicated
by the instrument will be equal to the one planned by the
transformer manufacturer for a given transformer load.
logon to www.scientificcontrols.com for further details
regarding OTI & WTI
| Is This Answer Correct ? | 33 Yes | 1 No |
Answer / sripellirajukumar
hi this is rajukumar
transformer testing engineer
actually in power transformer we will be using one sensor
that is WTA ..windidng temperature indicator..by that device
we can check the winding temperature of transformer.. when
the fault occures the winding temperature much be rised....
at that fault time this WTA will sence the obnormal
temperature of winding then it will send trip signal to the
ckt breaker...
but in heat run test we can not find the winding temperature
..but we can find how much the transfomer is heating on full
load current...
thanks..
| Is This Answer Correct ? | 18 Yes | 12 No |
Answer / pragati
hi I am Pragati
after reading those answers i found two keywords which are
RTD & thermostat.
RTD(resistance temperature detector) is used only to display
the temperature of winding. PT100 is one of RTD in which at
0degc the resistance is 100ohms. As temp. increases the
resistance increases linearly.
other is thermostat, it is an thermal switch.
DMP is one of thermostat which is having particular temp.
rating like 150deg C or 160 deg C and so on
as temp. of winding crosses the rated the switch is operated
and circuit is disconnected. This will protect our winding
from burning.
so if only display of temp. purpose we can use RTD & for
protection from burning we can use thermostat.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sunil
winding temp means temp. of oil plus additional temp
measure due to load
| Is This Answer Correct ? | 8 Yes | 4 No |
Mr Vishal u r write but i have confusion on equation
WTI= (Ambient Air Temperature) + (Top Oil Temp. Rise.) +
1.1 X GRADIENT
here what is GRADIENT?CAN WE COUNT GRADIENT VALUE?
IF U HAVE ANY IDEA THEN HELP ME TO ACHIEVE ANSWER.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shesh mani tiwari
winding gradient = (Iph)2 X RESISTANCE/OIL EXPOSED SURFACE
AREA.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / reddy
temparature sensors may be used.. sumpners test is heat run
test.. mean without any external loading, full load
testing of T/F
| Is This Answer Correct ? | 4 Yes | 6 No |
Answer / purushmallya
Generally RTDs i.e Resistance Temperature Detectors are
kept in core or winding which gives u temp of that spot.
| Is This Answer Correct ? | 5 Yes | 13 No |
why the earth conductor in top of the tranmission line ?
how to decide the rating of the ct for 1500 kva transformer
what are different types of alternator and discuss about the methods of cooling
16 Answers Bhel, Jindal, L&T, Nalco, Vedanta,
We have 110Vac ,10A ac supply which is converted into 110VDC & How much DC current? which factor is reqired for dc current calulation?
why the transformer neutral earthing is to be done by copper flat only,if we use GI flat what is the disadvantage.
Why have to use copper cable for local isolator to motor ?
how can we represne the analog signal and digital signal if want to measure the speed and we have to use PLC
what will happen if field winding of Synchronous generators given ac supply
if we want to convert the two 12 V DC batteries in parallel for UPS ? what would be the result ? which is better for a UPS , connect two batteries in series or connect them in parallel ?
check list of maintenance of transformer?
11 Answers ABC, Cosmos, EPRON, Essar, Godrej, Hescom, Infosys, KPTCL, TCS,
How many types of oil using in H/T & L/T Oil Circuit Breakers. need Explenation ?
when the rheostat kept in minimum to maximum position in motors what will happen?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)