why the transformer neutral earthing is to be done by copper
flat only,if we use GI flat what is the disadvantage.
Answers were Sorted based on User's Feedback
Answer / pradyumna chandra panda
Earth electrod should have low resistance and copper flate meet it. IF we use GI flate then potentional between earth &neutral will be increase on unbalance load, but it is allowed only 20 volt . we can decreare the earh resistance by increance the electrode in parallel.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / balu
Copper flat is low resistance than
compared to gi and it has good
mechanical strenth.
Is This Answer Correct ? | 1 Yes | 1 No |
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
Difference between earthing & grounding.?
motor and transformer working with same principle so why motor rotor was roted and transformer not roted
What is 2P*0.5 sqmm screened copper cable and what is the use of it..?
what do you mean by linear and bilateral network?
define displacement & magnitude ?
In 11/0.414 KV Parralel supply network with Bus tie closed what will be the fault level is it doubled or halved??
what is the difference between electrical wire and electrical conductor?
Why the airgap of an induction motor is less compared to that of a synchronous machine?
4 Answers MGVCL, RRB, WebTech,
What exactly is meant by harmonics and harmonic current?? and what is skewing with regard to this??
how a resistor resists to flow the current?how an inductor oppses the sudden change in current?how a capacitor opposes a DC voltage.
0 Answers Hindustan Unilever Limited,
what happens if you swap F1 and F2 connection in the exiter of the generator?