how we are measuring the winding temperature of the
transformer?
Answer Posted / purushmallya
Generally RTDs i.e Resistance Temperature Detectors are
kept in core or winding which gives u temp of that spot.
Is This Answer Correct ? | 5 Yes | 13 No |
Post New Answer View All Answers
how can calculate 1kva generator running time in 1 liter keroscene
how to calculate slip ring induction motor stator and rotor currents??
What is the Surge suppresor? Why using in a UDB's and How it works?
what is the effect of back reactive power on the generator ?
number of I/O devices in siemense plc
what is meant by neutral compensation factor and where it is used
In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
we use 400/5A ct and 35/roor3KV,/0.1/root3KV,0.1/root3KV pt ratio. What is the multiple factor of this meter.
what is the illumination level required for child play area?
star delta starter contorl circuit... drawing..
Load transfer in 11kv double busbar switchgear - operation.
what is the function of bearing in dc mchine" and where it is placed
What happens if i apply 500V to 440V rotary Switch ?
If Dg set load increase 25%, How much increase fuel Consumption (15 kva 2 cylinder DG set)