how we are measuring the winding temperature of the
transformer?
Answer Posted / sripellirajukumar
hi this is rajukumar
transformer testing engineer
actually in power transformer we will be using one sensor
that is WTA ..windidng temperature indicator..by that device
we can check the winding temperature of transformer.. when
the fault occures the winding temperature much be rised....
at that fault time this WTA will sence the obnormal
temperature of winding then it will send trip signal to the
ckt breaker...
but in heat run test we can not find the winding temperature
..but we can find how much the transfomer is heating on full
load current...
thanks..
Is This Answer Correct ? | 18 Yes | 12 No |
Post New Answer View All Answers
WHAT CAUSED THRESHOLD VOLTAGE TO EXIST?
Explain what is electric traction? Explain few advantages of electric traction system?
wat is d diffr btw shunt coil and trip coil in VCB?
how we decide wire gauge for ac or dc coil and what is the basic diff. B/w these two coil?
How is the percentage impedence of a transformer fixed at design stage???
send me any model test paper of clerical post of state bank of india.......
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
Is there any question in the name of Static Switch in UPS??
If a rotary UPS is in line through grid power; What would be the impact on Power Factor if the load through rotary ups is 25% , 50% , 75% & 100%. Will the power factor reduce with less load?
what is the standard values(Megger test) of resistances between L&N,L&E and N&E for a system on IEE regulations?
Connection diagram for KW meter and Kva meter
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases flux A does not alter B decreases C increases D none of above
The sodium vapor lamp is not glows when it is connected a distance of 5 meters above from gearbox, why ?
what is the use of sdf?
typically in power distribution substation. 1- Any idea how would be the graph of capacitor bank consumption verses time through the day . 2- How is the switching ( on and off ) of the capacitor bank, per need?