Answer / vijay khilnani
Dear Sripellirajukumar
I had answered 7 Amps and mentioned the thumb rule for
copper is 2000 Amps per sqaure Inch ( not 2000 Amps per sq
mm ) > You need to read the answer carefully before
commenting . For Your info 1 sq inch = 25.4 x 25.4 = 645 sq
mm. Also copper purity / type of insulation / temperature
rise allowed / voltage drop tolerarable would be other
factors which need to be considered. For this 2000 Amps / Sq
inch has a generous margin ie it is has some safety margin .
Vijay Khilnani
| Is This Answer Correct ? | 71 Yes | 17 No |
Answer / jokemaster
its the cable to carry the current and not the current to
carry the cable.:-)
| Is This Answer Correct ? | 38 Yes | 16 No |
Answer / ayad basha
The general thump rule is one square inch copper conductor
will carry 1000 Amps and that of for aluminium conductor is
600 Amps. So, for Cu, 1sqmm = 1.6 Amps appx. and for Al 1
sqmm = 0.9 Amps.
but this will not fit for the increasing cable sizez.
for example for 400Sqmm cable, it will not carry 400 x 1.6=
640 Amps. That is the effective current density of the
conductor decreases as the conductor size increase.
Also depth of cable laying, ambient temperature and cable
grouping also should be considered.
| Is This Answer Correct ? | 29 Yes | 17 No |
Answer / sripellirajukumar
ya mr vijay khilani ur answer might be correct but first u
have to mention the thumbrule ..instead of that u said rule
in ur first question..ok ur answer might be correct...
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / him
Around 15 Amp if cooling is natural . Thumbrule 6 Amp per
Sqmm
| Is This Answer Correct ? | 10 Yes | 8 No |
Answer / s.m murshed monowar
2.5 sqmm cu cable which voltage drop /mm is 9.7 ,it will
carry 16 amps maximum distance 30 meter & it will carry 20
amps for maximum distance 25 meter
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / npatra
It depends for which you are using.
1. Inside wall it's maximum capacity defined is 16Amp.
2. For Equipment its's Maximum Capacity defined to be 25Amp
| Is This Answer Correct ? | 4 Yes | 3 No |
How to use a insulation resistance tester on a three phase electric motor?
What is the difference between sensitive earth fault and restricted earth fault in power transformers?
can SMPS work in DC supply ?
10 Answers HCL, IBM, Reliance,
what is general test conduted by transformer
Which oil is used in Transformer?
what is pulverisation
why there is a high voltage line in multiplication of 11?i.e.- -66kv,11,kv,22kv
what is the difference between squirrel cage & slip ring induction motor?
17 Answers College School Exams Tests, NTPC, Ramyaa Electro Gear,
why we use ac system in india why not dc
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
Does Rheostat can use for power factor correction?
suri transmission
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)