Why capacitor bank does not require in DG Set?
Answers were Sorted based on User's Feedback
Answer / sudhir purandare
Basically the alternators are designed for 0.8 pF
only.Accrodingly the excitor voltage and current is
designed. You can not adjust the excitor voltage and
current to meet the power factor of load. This will
overload the alternator.
Is This Answer Correct ? | 53 Yes | 7 No |
Answer / sanjay dalvi
IN INDIA, DG DESIGN FOR 0.8 POWER FACTOR,THEN IN UR MIND A
QUESTION MAY ARRISE WHY .8 ONLY??
ANSWER IS THE LOAD IS ALLWAYS INDUCTIVE IN NATURE SO WE
USED 0.8 PF IN DG DEGINING AS A LAGGING PF.
NOW COME TO OUR ACTUAL QUESTION
CONSIDER 1000 KVA DG SET WHICH DELIVER 800 KW O/P POWER
BUT IF IMPROVE POWER FACTOR FROM .8 TO 1 PF THEN
OBEIOUSLY POWER DELIVER INCREGES FROM 800 TO 1000KW
P= V*I*COS $ WE KNOW THAT PF IS 1
LOAD CURRENT IS ALSO SAME FOR
LOAD
HERE POWER INCREASE DIRECTLY EFFECT THE VOLTAGE LEVEL
IF THE VOLTAGE LEVEL GOES BEYOND THE LIMIT IT WILL TRIP
THE AVR SYSTEM OF DG & DG WILL STOP RUNNING
IF WE USE CAPACITOR BANK THEN VOLTAGE LEVEL INCREASE
BEYOND THE LIMIT..SO WE R NOT USEING CAPACITOR BANK.
Is This Answer Correct ? | 24 Yes | 6 No |
Answer / ashish patil
sudhir answer is write. to avoid over loading we swiched
of capacitor bank.we dont control power factor through
exciter in case of DG.
Is This Answer Correct ? | 14 Yes | 7 No |
Answer / kj
In a single DG the power factor is not a function of the
DG. It is a function of the load. Inductive loads will
produce a lagging power factor and capacitive loads will
produce a leading power factor.
If a capacitor bank is used and the PF on the DG becomes
too far leading the fact that the voltage rise leads the
current rise in the waveform causes induced currents to
flow in the rotor field. This induced current replaces the
current produced by the AVR. As the PF becomes more leading
the AVR does not produce voltage and control of the voltage
is lost. The voltage will rise above the nominal settings
if the PF becomes more leading after the AVR has shut down.
So although it is not normal practice to use capacity banks
with DG's, they can be used as long as the PF remains
lagging.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / viswanath
we controlled the powerfactor though with exciter.that why
we not using the capacitor bank
Is This Answer Correct ? | 20 Yes | 16 No |
Answer / tapan
Increasing p.f shall automatically enhance the Kw demand
then its designed value and the alternator shall not be
able to cater this additional Kw and shall trip due to over
current. Hence it is not recommended to install the
capacitors accross the DG set to increase its p.f more then
its designed value.
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / gopinath madikeri
dr frnds, what Sudhir has said is right.. dg sets are built
with AVR(automatic voltage regulators) as it controlls the
voltage & power factor according to the load there will be
no requirement of seperate capacitor bank.
Is This Answer Correct ? | 5 Yes | 1 No |
DG set supplies necessary current to load. Its (internal)
Power Factor is governed by its design. DG sets like
transformers are rated in KVA i.e. KVxI.
Whatever be the load power factor, a DG set's internal power
factor will be governed by its design.
If a reactive load such as inductor or capacitor of
equivalent capacity (LOAD KVA = DG set's KVA)) is connected
across a DG set's terminals, the power factor measured at
these terminals will be nearly 0. However in this situation
also DG set's internal PF wikk be its designed PF.
Power factor is a parameter with respect to its measurement
location.
If load supplied by a DG set consists of large number of low
power factor loads which eats up only very small portion of
its total capacity and the balance load is taken by a high
power factor load, then the power factor at DG set's
terminal will still be high. But the DG set's internal power
factor will still be governed by its design.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sudhir purandare
DG set is a power source. Capacitor bank is required for a
load to maintain the power factor i.e. reactive power. The
alternators are designed for 0.8 pf. if the load pf is lower
than this value, it will overload alternator. under such
conditions it is necessary to install a capacitor bank.
Is This Answer Correct ? | 28 Yes | 26 No |
acb(AIR CIRCUIT BREAKER)NOT CHARGING AUTO
is that any software calculator to calculate the size of cable
For these 2 devices what their power ratings are ? 1) single phase : AC 220V & starting amps 3Amps (i.e. starting torque) and the stabilized amps 2A ... For deep freezer 2) single phase : AC 220V & starting amps 2.7Amps (i.e. including the starting torque of a CRT monitor) and the stabilized amps 1 Amps thanks
Which types of gate insttaled in static switch. Please give me answer.
why the star delta motors burn out frequently
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
what is the voltage regulation constant of ACSR Raccoon conductor
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
what is the abbreviation of MIMIC regarding control and relay panels of power systems????
How to calculate the Efficiency of Chiller
In HT overhead line why should provide top conducter which is not connected whith insulater..?
why rotor resistance starter is not suitable for squrielcage induction motor?why it is suitable for slipring induction motor?