Why capacitor bank does not require in DG Set?
Answers were Sorted based on User's Feedback
Answer / sudhir purandare
Basically the alternators are designed for 0.8 pF
only.Accrodingly the excitor voltage and current is
designed. You can not adjust the excitor voltage and
current to meet the power factor of load. This will
overload the alternator.
| Is This Answer Correct ? | 53 Yes | 7 No |
Answer / sanjay dalvi
IN INDIA, DG DESIGN FOR 0.8 POWER FACTOR,THEN IN UR MIND A
QUESTION MAY ARRISE WHY .8 ONLY??
ANSWER IS THE LOAD IS ALLWAYS INDUCTIVE IN NATURE SO WE
USED 0.8 PF IN DG DEGINING AS A LAGGING PF.
NOW COME TO OUR ACTUAL QUESTION
CONSIDER 1000 KVA DG SET WHICH DELIVER 800 KW O/P POWER
BUT IF IMPROVE POWER FACTOR FROM .8 TO 1 PF THEN
OBEIOUSLY POWER DELIVER INCREGES FROM 800 TO 1000KW
P= V*I*COS $ WE KNOW THAT PF IS 1
LOAD CURRENT IS ALSO SAME FOR
LOAD
HERE POWER INCREASE DIRECTLY EFFECT THE VOLTAGE LEVEL
IF THE VOLTAGE LEVEL GOES BEYOND THE LIMIT IT WILL TRIP
THE AVR SYSTEM OF DG & DG WILL STOP RUNNING
IF WE USE CAPACITOR BANK THEN VOLTAGE LEVEL INCREASE
BEYOND THE LIMIT..SO WE R NOT USEING CAPACITOR BANK.
| Is This Answer Correct ? | 24 Yes | 6 No |
Answer / ashish patil
sudhir answer is write. to avoid over loading we swiched
of capacitor bank.we dont control power factor through
exciter in case of DG.
| Is This Answer Correct ? | 14 Yes | 7 No |
Answer / kj
In a single DG the power factor is not a function of the
DG. It is a function of the load. Inductive loads will
produce a lagging power factor and capacitive loads will
produce a leading power factor.
If a capacitor bank is used and the PF on the DG becomes
too far leading the fact that the voltage rise leads the
current rise in the waveform causes induced currents to
flow in the rotor field. This induced current replaces the
current produced by the AVR. As the PF becomes more leading
the AVR does not produce voltage and control of the voltage
is lost. The voltage will rise above the nominal settings
if the PF becomes more leading after the AVR has shut down.
So although it is not normal practice to use capacity banks
with DG's, they can be used as long as the PF remains
lagging.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / viswanath
we controlled the powerfactor though with exciter.that why
we not using the capacitor bank
| Is This Answer Correct ? | 20 Yes | 16 No |
Answer / tapan
Increasing p.f shall automatically enhance the Kw demand
then its designed value and the alternator shall not be
able to cater this additional Kw and shall trip due to over
current. Hence it is not recommended to install the
capacitors accross the DG set to increase its p.f more then
its designed value.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / gopinath madikeri
dr frnds, what Sudhir has said is right.. dg sets are built
with AVR(automatic voltage regulators) as it controlls the
voltage & power factor according to the load there will be
no requirement of seperate capacitor bank.
| Is This Answer Correct ? | 5 Yes | 1 No |
DG set supplies necessary current to load. Its (internal)
Power Factor is governed by its design. DG sets like
transformers are rated in KVA i.e. KVxI.
Whatever be the load power factor, a DG set's internal power
factor will be governed by its design.
If a reactive load such as inductor or capacitor of
equivalent capacity (LOAD KVA = DG set's KVA)) is connected
across a DG set's terminals, the power factor measured at
these terminals will be nearly 0. However in this situation
also DG set's internal PF wikk be its designed PF.
Power factor is a parameter with respect to its measurement
location.
If load supplied by a DG set consists of large number of low
power factor loads which eats up only very small portion of
its total capacity and the balance load is taken by a high
power factor load, then the power factor at DG set's
terminal will still be high. But the DG set's internal power
factor will still be governed by its design.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / sudhir purandare
DG set is a power source. Capacitor bank is required for a
load to maintain the power factor i.e. reactive power. The
alternators are designed for 0.8 pf. if the load pf is lower
than this value, it will overload alternator. under such
conditions it is necessary to install a capacitor bank.
| Is This Answer Correct ? | 28 Yes | 26 No |
avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid after synchronisation it regulates power factor why....
how to protect motor in dol starter having capacity of 30 hp.40 hp?
can I improve the furnace power factor (10 mva transformer) by adding a capacitor bank before the transformer.Does system power factor vary a lot with the furnace PF?
Can we use Ccapacitive voltage transformer directly for metering purpose?
hi plz send me reliance placement papers..i.e electrical technical papers that have been asked in reliance test.
wha tis the ac motor used for traction system
we use 3 phase supply for induction motor why not use two phase supply .
how to calculate the minimum permissible limts of insulation resistance of switchyard equipments
what is the max. acceptable leakage current in 33kv bus bar
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise,give with best examples.... please help me in this regards....
what is the difference between brush & brushless dc motor explain its operation ?
Dear All, If we have 8No. 11kV cables running underground that are required to supply 20MW to a new development. What is the sustained current in Amps? Please advise.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)