HOw can we calculate power factor at HT side.
Answers were Sorted based on User's Feedback
Answer / joseph
Calculating Power Factor at LT or HT side is the same, as
P.F. is simply the ratio between the Active Power and
Apparent Power. Hence, if you have got both these
parameters then just divide Active Power by Apparent Power
(kW/KVA or MW/MVA as the case may be.)
| Is This Answer Correct ? | 26 Yes | 2 No |
Answer / k.shivkumar
Power factor can calculate KWH/KVAH readings
| Is This Answer Correct ? | 22 Yes | 6 No |
Answer / ashokreddyreguri
primary current is the vector sum of no load current and
load component of primary current
phase difference between primary current and primary
voltage gives primary power facter angle
primary power factor = cos (primary power facter angle)
primary power factor is always less than secondary power
factor
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / channaveer.s
# 2 Calculating Power Factor at LT or HT side is the same,
as
P.F. is simply the ratio between the Active Power and
Apparent Power. Hence, if you have got both these
parameters then just divide Active Power by Apparent Power
(kW/KVA or MW/MVA as the case may be.)
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / rohtash kathwalia
We can calculate Power factor by KW/ KVA. LT and HT power factor will be same.
| Is This Answer Correct ? | 1 Yes | 0 No |
In a d.c current, the power is the product of voltage and current. This relationship does not always apply to effective(r.m.s) values in an a.c circuit. Explain the reason for this.
What is excitation?
what dose the arrow indicate in the symbol of power transformer?
how the reverse power relay acts..
What will happen when we connect 2 bulbs in series between 2 phases
How check electrical motor winding.
When can we take Neutral as common neutral link?
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
what is carona and how is occur?
how to calulate multiplying factor if meter ratio is /5 ampere and ct ratio is 100/5 ampere.(our supply is 3 phase 415 volts)what is multiply factor?
what is the maximum rating(KVA) of transformer can be used in distribution side..(11KV/440v) and why??
When i went to a interview the interviewer ask me a question for that i cant able to answer him if anyone knows answer me How will you design a capacitor bank for a plant? if my p.f is 0.6 i have to improve it to 0.9 or 1 what kind of steps i have to do? and is there any formula for calculating this?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)