HOw can we calculate power factor at HT side.
Answers were Sorted based on User's Feedback
Answer / joseph
Calculating Power Factor at LT or HT side is the same, as
P.F. is simply the ratio between the Active Power and
Apparent Power. Hence, if you have got both these
parameters then just divide Active Power by Apparent Power
(kW/KVA or MW/MVA as the case may be.)
Is This Answer Correct ? | 26 Yes | 2 No |
Answer / k.shivkumar
Power factor can calculate KWH/KVAH readings
Is This Answer Correct ? | 22 Yes | 6 No |
Answer / ashokreddyreguri
primary current is the vector sum of no load current and
load component of primary current
phase difference between primary current and primary
voltage gives primary power facter angle
primary power factor = cos (primary power facter angle)
primary power factor is always less than secondary power
factor
Is This Answer Correct ? | 12 Yes | 5 No |
Answer / channaveer.s
# 2 Calculating Power Factor at LT or HT side is the same,
as
P.F. is simply the ratio between the Active Power and
Apparent Power. Hence, if you have got both these
parameters then just divide Active Power by Apparent Power
(kW/KVA or MW/MVA as the case may be.)
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / rohtash kathwalia
We can calculate Power factor by KW/ KVA. LT and HT power factor will be same.
Is This Answer Correct ? | 1 Yes | 0 No |
why the generator will take 8 to 12 hours to start after it got interrupted due to technical problems in case of power plants.
do any one help me to get "C" license,, i have doubts ,,, if mediators ter pls call me,, my no is 8056640042
what is interpose vt where it is used and y it is used?
How can we estimate Gen rotor current?
If i=10+10sin314t then find the rms and average value of current with explain?
Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp. ?
How many no of flip-flops are required to get 16 bit counter
how to calculate the megger values for motors and cables?
What is hysteresis losses?
How can decide the MVA rating of power transformer for substation like 220/132, 132/66, 66/33kv etc or even higher kv rating of substation???? Send me the strictly technical answer that shows your strong technical aptitude.
area control error
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.